Updated on 2025-12-18 GMT+08:00

Enabling Server WTP

Scenarios

The HSS web tamper protection (WTP) edition can protect dynamic and static web pages from being tampered with, enhancing the security and integrity of website content. It also includes the server protection capabilities of the premium edition, such as asset management, vulnerability detection, baseline check, intrusion detection, and ransomware protection, to detect attacks on servers.

This section describes how to enable Server WTP.

Prerequisites

Constraints

Before you enable protection for a Windows server, enable the Windows firewall to block the source IP addresses of brute-force attacks. If the Windows firewall is not enabled, HSS only generates alarms for detected brute-force attacks, but does not block them.
  • After the Windows firewall is enabled, HSS automatically adds firewall rules hostguard_AllowAnyIn and hostguard_AllowAnyOut to allow all inbound and outbound traffic. This ensures that the firewall does not affect your services. If HSS detects a brute-force attack, it adds an inbound rule to the firewall to block the attack source IP address. This does not affect your servers.
  • Do not disable the Windows firewall when using HSS, or HSS cannot block the source IP addresses of brute-force attacks. Once it is disabled, HSS may fail to block the attack source IP addresses even after you manually enable it again.

Enabling Web Tamper Protection

Server WTP can be enabled for one or multiple servers at a time. When you enable it for multiple servers at a time, the same protected directory settings will be applied to all of them, and cannot be customized for each server. If these servers have different directories to be protected, you can customize the protected directories or other settings for them separately after WTP is enabled. For details, see Modifying Server WTP Settings.

  1. Log in to the HSS console.
  2. Click in the upper left corner and select a region or project.
  3. In the navigation pane, choose Prevention > Web Tamper Protection.

    Figure 1 Web tamper protection

  4. On the Server WTP tab page, click the Servers tab. click Add Server.
  5. On the Add Server page, select servers and quotas, and click Next. For more information, see Table 1.

    Figure 2 Selecting servers
    Table 1 Parameters for selecting protected servers

    Parameter

    Description

    Example Value

    OS

    Select the OS type of the server to be protected by WTP.

    • Linux
    • Windows

    Linux

    Select Servers

    Select servers.

    You can filter the servers by software type or other attributes.

    -

    Select Quota

    The HSS WTP edition supports two billing modes, yearly/monthly and pay-per-use billing, to meet requirements in different scenarios.

    • Yearly/Monthly billing is a prepaid mode in which you pay for the service before using it. Your bill is generated based on the required duration you specify in the order. The longer you use the service, the more discounts you got.
    • Pay-per-use is a postpaid billing mode. You pay as you go and just pay for what you use. The HSS usage is calculated by the second but billed every hour. With the pay-per-use billing mode, you can easily adapt to resource requirement changes, reducing the risk of over-provisioning resources or lacking capacity. In this mode, there are no upfront commitments required.

    When selecting the yearly/monthly billing mode, you can select a quota or retain the default value Select a quota randomly.

    Yearly/Monthly

    Agreement

    Before enabling WTP, ensure that you have read the Host Security Service Disclaimer.

    Select I have read and agree to the Host Security Service Disclaimer.

    Selected

  6. On the Add Server page, configure policies. For more information, see Table 2.

    Figure 3 Configuring policies
    Table 2 Parameters for configuring rules

    Parameter

    Description

    Example Value

    Protected Directory

    Server WTP supports static and dynamic web page protection. Static WTP can lock protected directories, or restore their data from backups in real time once it detects changes made by attackers. Therefore, when configuring a protection policy, you need to specify the directories to be protected.

    After a directory is protected, the files and folders in the directory will become read-only.

    The requirements for adding a protected directory are as follows:

    • For Linux,
      • It cannot start with a space, end with a slash (/), or contain semicolons (;). Up to 256 characters are allowed.
      • A server can have up to 50 protected directories.
      • The folder levels of a protected directory cannot exceed 100.
      • The total folders in protected directories cannot exceed 900,000.
    • For Windows,
      • Up to 256 characters are allowed. The directory name cannot start with a space or end with a backslash (\). It cannot contain the following characters: ;/*?"<>|
      • A server can have up to 50 protected directories.

    Do not add network directories as protected directories. The reasons are as follows:

    • Inefficient detection

      A network directory usually contains a large number of files and may reach hundreds of terabytes, severely slowing down a scan.

    • Network bandwidth consumption

      Accessing a network directory consumes network bandwidth. A large-scale scan may fully occupy the network bandwidth and affect your workloads. For example, the access speed may slow down and the network latency may increase.

    • Linux: /etc/lesuo
    • Windows: d:\web

    Excluded Subdirectory (Optional)

    If a protected directory contains subdirectories that do not need to be protected, you can exclude the subdirectories.

    The requirements for adding a subdirectory are as follows:

    • Enter a subdirectory name or the relative subdirectory path under a protected directory. If you enter a subdirectory name, all subdirectories that match the name will be excluded, regardless of their levels.
    • A subdirectory name or path cannot start or end with a slash (/) and can contain up to 256 characters.
    • Up to 10 subdirectories can be added. Use semicolons (;) to separate multiple subdirectories.
    • Linux: data/cache or cache
    • Windows: web\test or test

    Excluded File Path (Optional)

    This item is available only for Linux servers.

    If a protected directory contains files that do not need to be protected, exclude the files.

    The requirements for adding excluded file paths are as follows:

    • Enter a file name or the relative file path under a protected directory. If you enter a file name, all files that match the name will be excluded, regardless of their levels.
    • A file name or path cannot start or end with a slash (/), and can contain up to 256 characters.
    • Up to 50 files can be added. Use semicolons (;) to separate multiple files.

    data/ma.txt or ma.txt

    Local Backup Path

    This item is available only for Linux servers.

    Set a local backup path for a protected directory. After WTP is enabled, files in the protected directory are automatically backed up to the local backup path. Once the system detects that a file in the protected directory is tampered with, it immediately uses the local backup to restore the tampered file.

    The requirements for adding local backup paths are as follows:

    • A local backup path cannot contain semicolons (;), start with a space, or end with a slash (/). Up to 256 characters are allowed.
    • Key system directories are a main attack target and cannot be used as backup paths, including but not limited to /etc/, /bin/, /usr/bin/, /var/spool/, /usr/sbin/, /sbin/, /usr/lib/, /lib/, /lib64/, /usr/lib64/, and their subdirectories.

    Local backup rule description:

    • The local backup path must be valid and cannot overlap with the protected directory path.
    • Excluded subdirectories and types of files are not backed up.
    • Generally, the backup completes within 10 minutes. The actual duration depends on the size of files in the protected directory.

    /backup

    Excluded File Type

    If a protected directory contains files of certain types that do not need to be protected, exclude these file types, for example, logs. You can exclude any type of files.

    To record the running status of servers in real time, exclude the log files in the protected directory. You can set high permission requirements for log read and write, so that attackers cannot view or tamper with log files.

    log

    Type

    Action taken when file tampering is detected.

    • Alarm: Only alarms are reported.
    • Block: An alarm is reported, and the file is restored to the status before being tampered with.

    Block

    Scheduled Protection (Optional)

    You can schedule when to disable static WTP. In the unprotected period, you can modify, update, or release web pages.

    Click to enable scheduled protection and configure the following parameters:

    • Unprotected Time Range

      A time range when WTP is disabled within a day, for example, 10:05 to 15:35.

      Requirements:

      • A time range must be at least 5 minutes.
      • Time ranges (except for those starting at 00:00 or ending at 23:59) cannot overlap and must have at least a 5-minute interval.
      • All time ranges are subject to the system time of the server.
    • Unprotected Days of a Week

      Static WTP is automatically disabled on specified days of a week, for example, Wednesday and Thursday.

    , 10:05-15:35, Wednesday

    Dynamic WTP (Optional)

    Dynamic WTP is mainly used to protect Tomcat applications on Linux. It can detect and prevent tampering with dynamic data, such as database data, in real time during application running.

    Currently, dynamic WTP can protect Tomcat applications using JDK 8, JDK 11, and JDK 17.

    To enable dynamic WTP, click and enter a complete Tomcat bin directory path, for example, /usr/workspace/apache-tomcat-8.5.15/bin. The system presets the setenv.sh script in the bin directory to configure the startup parameters of the anti-tamper program.

    , /usr/workspace/apache-tomcat-8.5.15/bin

    Configure Privileged Processes (Optional)

    A privileged process is a process authorized to modify a protected directory.

    You can configure privileged processes in the following scenarios:

    • File modification protection

      If WTP is enabled, all files in protected directories are set to read-only and cannot be modified. You can add privileged processes and use them to modify the files in protected directories or update websites. Ensure the specified privileged processes, which are authorized to access protected directories, are secure and reliable.

    • Tampering behavior tracing

      If you enable web tamper protection for a Linux server, you can configure privileged processes to record the information, such as process IDs and commands, of processes that trigger tampering.

    This feature is compatible with Linux and Windows. For Linux, only the distributions using kernel versions 5.10 or later are supported.

    Click to enable the privileged processes and configure the following parameters:

    • Process File Path

      Set one or multiple complete file paths of privileged processes. Put each privileged process file path on a separate line. Up to 10 privileged processes are allowed.

    • Trust Subprocess

      If Trust Subprocess is enabled, HSS will trust all the subprocesses up to five levels deep in the subdirectories of specified directories, and allow the subprocesses to modify protected directories, and allow the subprocesses to modify protected directories.

    • Linux: /Path/Software.type
    • Windows: C:\Path\Software.type

  7. After the policy is configured, click OK.
  8. On the Servers tab, check the static and dynamic WTP status of the server.

    The Protected status indicates protection has been enabled. After dynamic WTP is enabled, restart Tomcat to apply the settings.

    After the protection is enabled, it takes 2 to 3 minutes for HSS to send protection policies to agents. The protection is successful only after all policies are sent. To check policy statuses, choose Asset Management > Servers & Quota and click a server name. On the server details page, choose Security Operations > Policies. If all the policy statuses are Enabled, the policies have been sent.

  9. (Optional) Configure alarm notification, protection policies, server login protection, and malicious program isolation and removal.

    In addition to web tamper protection, the HSS WTP edition also offers server protection, vulnerability scan, and baseline check functions. For details about the functions, see Features. You can configure them as needed. Below are the ways to configure basic features:

Advanced Defense Functions

The HSS WTP edition provides a series of advanced defense functions. You can enable them as needed to enhance server security. For details, see Table 4.

Table 3 Advanced defense functions

Function

Description

Application Protection

To protect your applications with RASP, you simply need to add probes to them, without having to modify application files.

Ransomware Prevention

The function can detect and defend against ransomware. It can automatically back up data either at a scheduled time, or immediately if ransomware is detected. This can help you defend against ransomware and reduce loss.

Ransomware prevention is automatically enabled with the container edition. HSS will deploy honeypot files on servers and automatically isolate suspicious encryption processes. You can modify the ransomware protection policy. You are also advised to enable backup so that you can restore data.

Application Process Control

Application process control helps to enhance the security of applications and processes running on servers. It can automatically identify and analyze application processes, and classify them into trusted, suspicious, and malicious processes. It allows trusted processes to run, and generates alarms for suspicious and malicious processes. This helps to build a secure environment for application processes, and protects servers from untrusted or malicious application processes.

Virus Scanning and Removal

This function combines cloud-based and local antivirus mechanisms to scan executable files, compressed files, scripts, documents, images, and audiovisual files for viruses. You can perform quick scan, full-disk scan, and custom scans on servers as needed to detect and remove virus files in a timely manner, enhancing the virus defense of the system.

Dynamic Port Honeypot

The dynamic port honeypot function is a proactive defense measure. It uses a real port as a honeypot port to induce attackers to access the network. In the horizontal penetration scenario, the function can effectively detect attackers' scanning, identify faulty servers, and protect real resources of the user.