Help Center/ Cloud Container Engine/ User Guide/ O&M/ O&M Best Practices/ Monitoring Master Node Components with Prometheus
Updated on 2026-09-21 GMT+08:00
This section describes how to monitor the kube-apiserver, kube-controller, kube-scheduler, kubelet-cadvisor-master, and etcd-server components on master nodes using Prometheus.
Viewing the Metrics of Master Node Components in Monitoring Center
Monitoring Center can monitor the kube-apiserver component on the master nodes. After you enable Monitoring Center, the Cloud Native Cluster Monitoring add-on (Cloud Native Cluster Monitoring) of version 3.5.0 or later is installed, and you can view the API metrics in the API server view (API Server View) on the dashboard.
To monitor the kube-controller, kube-scheduler, kubelet-cadvisor-master, and etcd-server components, take the following steps.
  • Basic container metrics do not include data from kube-controller-manager, kube-scheduler, or etcd-server. Once Monitoring Center reports these metrics to AOM, you will incur additional charges. Therefore, Monitoring Center does not collect these component metrics by default.
  • The kubelet-cadvisor-master component collects cAdvisor metrics from the master node's kubelet, filters by container=kube-apiserver, and exposes only the kube-apiserver container metrics.
    To collect metrics from the kubelet-cadvisor-master component, the cluster version must be v1.30.14-r90, v1.31.14-r50, v1.32.13-r20, v1.33.12-r0, v1.34.8-r0, v1.35.5-r0, v1.36.1-r10, or later, and the Cloud Native Cluster Monitoring version must be 3.12.15 or later.
  2. In the navigation pane, choose Settings. Then, click the Monitoring tab and modify collection settings.
    • If Preset Policies is enabled, Cloud Native Cluster Monitoring includes preset collection policies for some components. You can click Manage under Preset Policies to enable metric collection for the kube-apiserver, kube-controller, kube-scheduler, kubelet-cadvisor-master, and etcd-server components. You can also select All metrics or Trustlist metrics as needed. This helps control AOM data collection costs.
    • If Preset Policies is not enabled, Cloud Native Cluster Monitoring automatically creates ServiceMonitor policies for master node components. You can click Manage under ServiceMonitor Policies to enable metric collection for the kube-apiserver, kube-controller, kube-scheduler, kubelet-cadvisor-master, and etcd-server components. By default, only trustlist metrics are collected.
      By default, the ServiceMonitor policies automatically created by the Cloud Native Cluster Monitoring add-on collect some metrics in the trustlist. If the metrics cannot meet your requirements, enable Preset Policies and create custom metrics.
  3. Wait for 5 minutes and go to the AOM console. On the Metric Browsing page, locate the AOM instance that the component metrics are reported to and view the metrics of the preceding components. For more metric details, see kube-apiserver Metrics, kube-controller Metrics, kube-scheduler Metrics, kubelet-cadvisor-master Metrics, and etcd-server Metrics.
    Figure 1 Viewing metrics
Collecting the Metrics of Master Node Components Using Self-Built Prometheus
This section describes how to collect the metrics of master node components using self-built Prometheus.
  • The cluster version must be 1.19 or later. To collect metrics from the kubelet-cadvisor-master component, the cluster version must be v1.30.14-r90, v1.31.14-r50, v1.32.13-r20, v1.33.12-r0, v1.34.8-r0, v1.35.5-r0, v1.36.1-r10, or later.
  • You need to install self-built Prometheus using Helm by referring to Prometheus. You need to use prometheus-operator to manage the installed Prometheus by referring to Prometheus Operator.
    Because the Prometheus add-on (Prometheus (EOM)) is end of maintenance and does not support this function, you are advised not to use this add-on.
  1. Use kubectl to access the cluster.
  2. Modify the ClusterRole of Prometheus.
    kubectl edit ClusterRole prometheus -n {namespace}
    Add the following content under the rules field:
    rules:
    - apiGroups:
      - proxy.exporter.k8s.io
      resources:
      verbs: ["get", "list", "watch"]
  3. Create a file named kube-apiserver.yaml and edit it.
    vi kube-apiserver.yaml
    Example file content:
    apiVersion: monitoring.coreos.com/v1
    kind: ServiceMonitor
      labels:
        app.kubernetes.io/name: apiserver
      namespace: monitoring    # Change it to the namespace where Prometheus will be installed.
      endpoints:
      - bearerTokenFile: /var/run/secrets/kubernetes.io/serviceaccount/token
        interval: 30s
        metricRelabelings:
        - action: keep
          regex: (aggregator_unavailable_apiservice|apiserver_admission_controller_admission_duration_seconds_bucket|apiserver_admission_webhook_admission_duration_seconds_bucket|apiserver_admission_webhook_admission_duration_seconds_count|apiserver_client_certificate_expiration_seconds_bucket|apiserver_client_certificate_expiration_seconds_count|apiserver_current_inflight_requests|apiserver_request_duration_seconds_bucket|apiserver_request_total|go_goroutines|kubernetes_build_info|process_cpu_seconds_total|process_resident_memory_bytes|rest_client_requests_total|workqueue_adds_total|workqueue_depth|workqueue_queue_duration_seconds_bucket|aggregator_unavailable_apiservice_total|rest_client_request_duration_seconds_bucket)
          sourceLabels:
          - __name__
        - action: drop
          regex: apiserver_request_duration_seconds_bucket;(0.15|0.25|0.3|0.35|0.4|0.45|0.6|0.7|0.8|0.9|1.25|1.5|1.75|2.5|3|3.5|4.5|6|7|8|9|15|25|30|50)
          sourceLabels:
          - __name__
          - le
        port: https
        scheme: https
        tlsConfig:
          caFile: /var/run/secrets/kubernetes.io/serviceaccount/ca.crt
          serverName: kubernetes
      jobLabel: component
      namespaceSelector:
        matchNames:
        - default
      selector:
        matchLabels:
          component: apiserver
          provider: kubernetes
    Create a ServiceMonitor:
    kubectl apply -f kube-apiserver.yaml
  4. Create a file named kube-controller.yaml and edit it.
    vi kube-controller.yaml
      labels:
        app.kubernetes.io/name: kube-controller
      endpoints:
          interval: 15s
          honorLabels: true
          port: https
          relabelings:
            - regex: (.+)
              replacement: /apis/proxy.exporter.k8s.io/v1beta1/kube-controller-proxy/${1}/metrics
              sourceLabels:
                - __address__
              targetLabel: __metrics_path__
            - regex: (.+)
              replacement: ${1}
              sourceLabels:
                - __address__
              targetLabel: instance
            - replacement: kubernetes.default.svc.cluster.local:443
              targetLabel: __address__
          scheme: https
          tlsConfig:
      jobLabel: app
      namespaceSelector:
        matchNames:
          - kube-system
      selector:
        matchLabels:
          app: kube-controller-proxy
          version: v1
    kubectl apply -f kube-controller.yaml
  5. Create a file named kube-scheduler.yaml and edit it.
    vi kube-scheduler.yaml
      labels:
        app.kubernetes.io/name: kube-scheduler
      endpoints:
          interval: 15s
          honorLabels: true
          port: https
          relabelings:
            - regex: (.+)
              replacement: /apis/proxy.exporter.k8s.io/v1beta1/kube-scheduler-proxy/${1}/metrics
              sourceLabels:
                - __address__
            - regex: (.+)
              replacement: ${1}
              sourceLabels:
                - __address__
          scheme: https
          tlsConfig:
      jobLabel: app
      namespaceSelector:
        matchNames:
          - kube-system
      selector:
        matchLabels:
          app: kube-scheduler-proxy
          version: v1
    kubectl apply -f kube-scheduler.yaml
  6. Create a file named etcd-server.yaml and edit it.
    vi etcd-server.yaml
      labels:
        app.kubernetes.io/name: etcd-server
      endpoints:
          interval: 15s
          honorLabels: true
          port: https
          relabelings:
            - regex: (.+)
              replacement: /apis/proxy.exporter.k8s.io/v1beta1/etcd-server-proxy/${1}/metrics
              sourceLabels:
                - __address__
            - regex: (.+)
              replacement: ${1}
              sourceLabels:
                - __address__
          scheme: https
          tlsConfig:
      jobLabel: app
      namespaceSelector:
        matchNames:
          - kube-system
      selector:
        matchLabels:
          app: etcd-server-proxy
          version: v1
    kubectl apply -f etcd-server.yaml
  7. Create and edit kubelet-cadvisor-master.yaml.
    vi kubelet-cadvisor-master.yaml
    The file content is as follows:
      labels:
        app.kubernetes.io/name: kubelet-cadvisor-master
      namespace: monitoring    # Replace it with your Prometheus namespace.
      endpoints:
          honorLabels: true
          metricRelabelings:
            - action: keep
              regex: (container_cpu_usage_seconds_total|container_memory_working_set_bytes|container_spec_cpu_quota|container_spec_memory_limit_bytes)
              sourceLabels:
                - __name__
          port: https
          relabelings:
            - action: replace
              regex: (.+)
              replacement: /apis/proxy.exporter.k8s.io/v1beta1/kubelet-cadvisor-master-proxy/${1}/metrics
              sourceLabels:
                - __address__
            - action: replace
              regex: (.+)
              replacement: ${1}
              sourceLabels:
                - __address__
            - action: replace
            - action: replace
              replacement: kubelet-cadvisor-master
              targetLabel: job
          scheme: https
          tlsConfig:
      namespaceSelector:
        matchNames:
          - kube-system
      selector:
        matchLabels:
          app: kubelet-cadvisor-master-proxy
    Create a ServiceMonitor.
    kubectl apply -f kubelet-cadvisor-master.yaml
  8. Access Prometheus and choose Status > Targets. The preceding master node components are displayed.
Category
Metric
Type
Example PromQL Statement
Request metrics
Counter
The total number of API requests received by kube-apiserver, broken down by labels.
Example labels:
  • verb: HTTP request method, such as GET, POST, PUT, DELETE, PATCH, LIST, or WATCH.
  • group: Kubernetes API group, such as apps/v1 or networking.k8s.io/v1.
  • version: API version, such as v1 or v1beta1.
  • resource: Kubernetes resource type, such as pods, Deployments, Services, or nodes.
  • subresource: sub-resource of a resource (some operations are only available for sub-attributes of the resource), such as logs (viewing logs), exec (executing commands), or status (updating status).
  • scope: application scope of a request, such as cluster (cluster-level), namespace (namespace-level), or resource (single resource).
  • component: source component of a request, such as kube-controller-manager or kube-scheduler.
  • client: the client that initiates a request. It may be an internal component or an external service.
  • code: HTTP response status code, such as 200 (OK), 404 (Not Found), 500 (Internal Server Error), or 429 (Too Many Requests).
  • To query the total request rate (measured by QPS):
    sum(rate(apiserver_request_total[5m]))
  • To query the request errors (5xx returned):
    sum(rate(apiserver_request_total{code=~"5.."}[5m])) by (resource, verb)
  • To query the requests subject to rate limiting (status code 429)
    sum(rate(apiserver_request_total{code="429"}[5m])) by (resource)
  • To query the clients that frequently send requests:
    topk(5, sum(rate(apiserver_request_total[5m])) by (client))
Histogram
Response latency distribution, broken down by labels (such as request type, resource, and status code). This metric can be used to analyze P50, P90, and P99 latencies, identify slow requests and high-latency resources, and monitor kube-apiserver performance.
Example labels:
  • le: core label of the histogram. It indicates the number of requests that took less than or equal to an interval (measured in seconds). For example, le="0.005" indicates the number of requests that took less than or equal to 5 ms.
  • To query the P99 latency (99% of the requests completed within given latency):
    histogram_quantile(0.99,sum(rate(apiserver_request_duration_seconds_bucket[5m])) by (le, resource, verb))
    Example output:
    {resource="pods", verb="GET"}    0.8  # 99% of GET requests for pods completed within 0.8s
    {resource="deployments", verb="POST"} 1.2 # 99% of POST requests for deployments completed within 1.2s
  • To query the P90 latency by resource type:
    histogram_quantile(0.90,sum(rate(apiserver_request_duration_seconds_bucket[5m])) by (le, resource))
    Example output:
    {resource="pods"}      0.5  # 90% of pod requests completed within 0.5s
    {resource="services"}  0.3  # 90% of Service requests completed within 0.3s
  • To monitor high-latency requests (> 1s):
    sum(rate(apiserver_request_duration_seconds_bucket{le="+Inf"}[5m])) by (resource, verb)- sum(rate(apiserver_request_duration_seconds_bucket{le="1.0"}[5m])) by (resource, verb)
    Example output:
    {resource="pods", verb="LIST"}  50  # 50 LIST requests for pods took longer than 1s in the last 5 minutes
Gauge
The number of API requests that are being executed. This metric typically contains the following labels:
  • readOnly: read requests, which do not change the cluster status. Read requests are usually used to read resources, for example, obtaining the pod list and querying the node status.
  • mutating: write requests, which change the cluster status. Write requests are usually used to create, update, or delete resources, for example, creating a pod or updating a Service.
  • To view the number of write requests that are being executed:
    apiserver_current_inflight_requests{request_kind="mutating"}
  • To view the number of read requests that are being executed:
    apiserver_current_inflight_requests{request_kind="readOnly"}
  • To view the total number of requests that are being executed:
    sum(apiserver_current_inflight_requests)
etcd_request_duration_seconds_bucket
Histogram
etcd request latency.
Example labels:
  • type: type of the operation object.
  • operation: operation type.
  • To query P99 latency:
    histogram_quantile(0.99,sum(rate(etcd_request_duration_seconds_bucket[5m])) by (le, type))
  • To compare read and write latencies:
    histogram_quantile(0.95,rate(etcd_request_duration_seconds_bucket{type=~"range|put"}[5m]))
  • To detect slow requests (> 1s):
    sum(rate(etcd_request_duration_seconds_bucket{le="+Inf"}[5m]))  - sum(rate(etcd_request_duration_seconds_bucket{le="1"}[5m]))
Error and rate limiting metrics
apiserver_flowcontrol_current_executing_requests
Gauge
One of the core metrics in API Priority and Fairness (APF). It reflects the number of requests being executed by the API server in real time. For details, see API Priority and Fairness.
Example labels:
  • priority_level: request priority level. Options:
    • exempt: used for requests that are not subject to flow control (such as requests for key system operations). Requests of this priority level do not occupy the concurrency quota.
    • system: used for requests from Kubernetes control plane components (such as kube-controller-manager and kube-scheduler)
    • node-high: used for health status updates from nodes.
    • leader-election: used for leader election requests (such as requests from kube-controller-manager).
    • workload-high/low: used for workload requests with high and low priorities, respectively.
    • global-default: used for default requests that do not match any FlowSchemas.
    • catch-all: (default) used for all requests that are not explicitly classified. Requests of this priority have a very low concurrency quota.
  • flow_schema: the FlowSchema that matches requests. A FlowSchema can identify the request source (such as kube-controller-manager or kube-scheduler).
  • To view the number of requests executed by priority level:
  • To query resource usages by priority level:
    sum(apiserver_flowcontrol_current_executing_requests{priority_level=~"system|leader-election"}) / sum(apiserver_flowcontrol_nominal_limit_seats{priority_level=~"system|leader-election"})
apiserver_flowcontrol_current_inqueue_requests
Gauge
The number of requests waiting to be executed in the flow control queue. These requests have been received but are not executed because the number of concurrent requests has reached the configured limit. For details, see API Priority and Fairness.
Example labels:
  • priority_level: request priority level (such as system or workload-high).
  • To identify stacked requests labeled by system:
    apiserver_flowcontrol_current_inqueue_requests{priority_level="system"}
  • To identify requests that are stacked within 5 minutes:
    delta(apiserver_flowcontrol_current_inqueue_requests[5m])
Gauge
The nominal request concurrency limit per priority level. For details, see API Priority and Fairness.
This metric is classified by the priority_level label, which indicates the request priority level (such as system or workload-high).
  • To view the nominal request concurrency limits for all priority levels:
  • To calculate resource usages based on executing requests:
    sum(apiserver_flowcontrol_current_executing_requests) by (priority_level) / apiserver_flowcontrol_nominal_limit_seats
apiserver_flowcontrol_current_limit_seats
Gauge
The request concurrency limit per priority level. This metric allows you to learn the load of the API server and determine whether to adjust the traffic control policy in high-load scenarios. For details, see API Priority and Fairness.
Unlike nominal_limit_seats, the value of this metric may be affected by the global traffic control policy.
To view the request concurrency limit at a priority level:
apiserver_flowcontrol_current_limit_seats{priority_level="system"}
apiserver_flowcontrol_current_executing_seats
Gauge
The number of seats corresponding to the requests currently being executed in a priority queue. This metric reflects the concurrent resources being consumed in the queue and helps you understand the actual load of the queue. For details, see API Priority and Fairness. This metric is classified by the priority_level label, which indicates the request priority level (such as system or workload-high).
If the value of current_executing_seats is close to that of current_limit_seats, the concurrent resources of the queue may be about to be used up. You can increase max-mutating-requests-inflight and max-requests-inflight to optimize performance. For details, see Modifying Cluster Configurations.
  • To view the number of concurrent seats that have been occupied for a specific priority level:
    apiserver_flowcontrol_current_executing_seats{priority_level="system"}
  • To calculate the seat usage (current usage/current limit):
    sum(apiserver_flowcontrol_current_executing_seats) by (priority_level) / sum(apiserver_flowcontrol_current_limit_seats) by (priority_level)
apiserver_flowcontrol_current_inqueue_seats
Gauge
The concurrent resources consumed by the requests waiting in queues for all priority levels. For details, see API Priority and Fairness.
  • To view the seats occupied by requests waiting in the queue for a specific priority level:
    apiserver_flowcontrol_current_inqueue_seats{priority_level="system"}
  • To calculate the percentage of queued requests (the number of queued seats/total concurrency quota):
    sum(apiserver_flowcontrol_current_inqueue_seats) by (priority_level)/sum(apiserver_flowcontrol_nominal_limit_seats) by (priority_level)
apiserver_flowcontrol_request_execution_seconds_bucket
Histogram
The execution time of API requests. For details, see API Priority and Fairness.
Example labels:
  • To calculate the execution time for 99% of requests:
    histogram_quantile(0.99,  sum(rate(apiserver_flowcontrol_request_execution_seconds_bucket[5m])) by (le, priority_level))
    sum(rate(apiserver_flowcontrol_request_execution_seconds_bucket{le="+Inf"}[5m]))- sum(rate(apiserver_flowcontrol_request_execution_seconds_bucket{le="1"}[5m]))
apiserver_flowcontrol_request_wait_duration_seconds_bucket
Histogram
The waiting time of API requests in a queue. For details, see API Priority and Fairness.
Example labels:
  • To calculate the waiting time for 95% of requests:
    histogram_quantile(0.95,  sum(rate(apiserver_flowcontrol_request_wait_duration_seconds_bucket[5m])) by (le, priority_level))
  • To detect long-lasting requests (> 5s):
    sum(rate(apiserver_flowcontrol_request_wait_duration_seconds_bucket{le="+Inf"}[5m]))- sum(rate(apiserver_flowcontrol_request_wait_duration_seconds_bucket{le="5"}[5m]))
apiserver_flowcontrol_dispatched_requests_total
Counter
The total number of API requests that have been scheduled (started to be executed). For details, see API Priority and Fairness.
  • To calculate the request rate at each priority level:
    sum(rate(apiserver_flowcontrol_dispatched_requests_total[5m])) by (priority_level)
  • To compare the number of requests in different FlowSchemas:
    sum(rate(apiserver_flowcontrol_dispatched_requests_total[5m])) by (flow_schema)
apiserver_flowcontrol_rejected_requests_total
Counter
The total number of rejected API requests. Requests are often rejected due to traffic control or insufficient resources. For details, see API Priority and Fairness.
Example labels:
  • reason: the reason why a request is rejected. Options:
    • queue-full: Too many requests were already queued.
    • concurrency-limit: If the number of requests exceeds the concurrency limit, the extra requests will be rejected. The excess traffic is immediately rejected with HTTP 429 (Too Many Requests).
    • time-out: The request was still in the queue when its queuing time expired.
    • cancelled: The request was not purged and locked and has been ejected from the queue.
  • To calculate the request rejection rate:
    sum(rate(apiserver_flowcontrol_rejected_requests_total[5m])) by (priority_level, reason)
  • To calculate the rejection rate ratio:
    sum(rate(apiserver_flowcontrol_rejected_requests_total[5m])) by (priority_level)/sum(rate(apiserver_flowcontrol_dispatched_requests_total[5m])) by (priority_level)
apiserver_flowcontrol_request_concurrency_limit
Gauge
The maximum number of concurrent requests for a priority queue.
This metric is deprecated in Kubernetes 1.30 and removed from Kubernetes 1.31. You are advised to use apiserver_flowcontrol_nominal_limit_seats in clusters of v1.31 or later.
To view the current global concurrency limit:
Authentication and authorization metrics
Histogram
The time that the admission controller takes to process API requests.
Example labels:
  • name: name of the admission controller that processes requests, such as MutatingAdmissionWebhook or ValidatingAdmissionWebhook.
  • operation: operation, such as CREATE, UPDATE, or DELETE.
  • type: operation type.
    • validate: validates the validity of a request.
    • admit: controls whether to allow a valid request.
  • rejected: controls whether a request is rejected. The value can be true or false.
  • To sort the results by controller name:
    sort_desc(histogram_quantile(0.99,rate(apiserver_admission_controller_admission_duration_seconds_bucket[5m])))
  • To calculate the processing time for 99% of requests:
    histogram_quantile(0.99,sum(rate(apiserver_admission_controller_admission_duration_seconds_bucket[5m])) by (le, name))
Histogram
The time that the admission webhook takes to process requests.
histogram_quantile(0.99,sum(rate(apiserver_admission_webhook_admission_duration_seconds_bucket[5m])) by (le, name))
Service availability metrics
up
Gauge
Service availability. Options:
  • 1: A service is available.
  • 0: A service is unavailable.
To check the availability of the current service:
up
Metric
Type
Counter
The number of adds processed by the workqueue.
  • To calculate the task addition rate of each queue:
    rate(workqueue_adds_total[5m])
  • To detect the abnormal high addition rate (> 1,000/minute):
    rate(workqueue_adds_total[1m]) > 1000/60
  • To sort the results by controller:
    topk(3, sum by(name) (rate(workqueue_adds_total[5m])))
workqueue_depth
Gauge
How big the workqueue is. If the queue depth remains high for a long time, the controller cannot process tasks in the queue in a timely manner, causing task stacking.
To view the depths of all queues:
workqueue_depth
Histogram
How long in seconds a task stays in the workqueue before being executed.
Example labels:
  • name: task name.
  • To calculate the queuing time for 99% of requests:
    histogram_quantile(0.99,  rate(workqueue_queue_duration_seconds_bucket[5m]))
  • To detect long-lasting tasks (> 10s):
    sum(rate(workqueue_queue_duration_seconds_bucket{le="+Inf"}[5m])) - sum(rate(workqueue_queue_duration_seconds_bucket{le="10"}[5m]))
Counter
The number of HTTP requests initiated by the Kubernetes client.
Example labels:
  • host: host address.
  • method: HTTP request method, such as GET, POST, PUT, DELETE, PATCH, LIST, or WATCH.
  • To calculate the request rate (by status code):
    sum by(code) (rate(rest_client_requests_total[5m]))
  • To detect the 5xx error rate:
    rate(rest_client_requests_total{code=~"5.."}[5m]) / rate(rest_client_requests_total[5m])
  • To collect request statistics by target service:
    sum by(host) (rate(rest_client_requests_total[5m]))
Histogram
The latency of HTTP requests from the client.
Example labels:
  • To calculate the P95 latency:
    histogram_quantile(0.95,  rate(rest_client_request_duration_seconds_bucket[5m]))
  • To detect slow requests (> 2s):
    sum(rate(rest_client_request_duration_seconds_bucket{le="+Inf"}[5m]))- sum(rate(rest_client_request_duration_seconds_bucket{le="2"}[5m]))
Metric
Type
scheduler_scheduler_cache_size
Gauge
The number of nodes, pods, and assumed pods (pods to be scheduled) in the scheduler cache.
To view the number of cached pods:
scheduler_scheduler_cache_size{type="pod"}
scheduler_pending_pods
Gauge
The number of pending pods. This metric can be used to identify scheduling bottlenecks.
This metric is usually classified by the following queue labels:
  • active: the number of pods that are ready and waiting for scheduling.
  • backoff: the number of pods that fail to be scheduled.
  • gated: the number of pods that have been scheduled but declared unschedulable, or explicitly marked as unschedulable.
  • unschedulable: the number of pods that cannot be scheduled.
To view the number of pods in a specific queue:
scheduler_pending_pods{queue="backoff"}
scheduler_pod_scheduling_attempts_bucket
Histogram
The number of attempts to schedule a pod.
Generally, this metric is labeled by le. The value can be 1, 2, 4, 8, 16, or +Inf.
To detect high-frequency retries (more than eight attempts):
sum(rate(scheduler_pod_scheduling_attempts_bucket{le="+Inf"}[5m]))- sum(rate(scheduler_pod_scheduling_attempts_bucket{le="8"}[5m]))
etcd-server Metrics
Category
Metric
Type
etcd leader status metrics
etcd_server_has_leader
Gauge
etcd elects a member in a cluster as the leader (master node) and other members as followers (slave nodes). The leader periodically sends heartbeats to all members for cluster stability.
This metric controls whether there is a leader among the etcd servers. Options:
  • 1: There is a leader among the etcd servers.
  • 0: There is no leader among the etcd servers.
To view the leader status:
etcd_server_is_leader
Gauge
Whether an etcd member is the leader. Options:
  • 1: The etcd member is the leader.
  • 0: The etcd member is not the leader.
To check whether an etcd member is the leader:
etcd_server_leader_changes_seen_total
Counter
The number of leader changes within a specific period of time.
To monitor the leader change frequency within 1 hour:
rate(etcd_server_leader_changes_seen_total[1h])
etcd storage metrics
etcd_mvcc_db_total_size_in_bytes
Gauge
The total size of etcd.
To calculate the storage space usage:
etcd_mvcc_db_total_size_in_use_in_bytes  / etcd_mvcc_db_total_size_in_bytes
Gauge
The usage of etcd.
etcd_debugging_mvcc_keys_total
Gauge
The total number of keys in etcd.
To monitor the increase of keys:
rate(etcd_debugging_mvcc_keys_total[5m])
etcd write performance metrics
etcd_disk_backend_commit_duration_seconds_bucket
Histogram
Time required by the etcd for data at rest. This is the time that the etcd takes to write a data change to the storage backend and commit data.
To calculate the P99 latency for writes:
histogram_quantile(0.99,rate(etcd_disk_backend_commit_duration_seconds_bucket[5m]))
etcd_server_proposals_committed_total
Gauge
The number of proposals submitted by the etcd.
To calculate the write failure rate:
rate(etcd_server_proposals_failed_total[5m]) / rate(etcd_server_proposals_committed_total[5m])
etcd_server_proposals_applied_total
Gauge
The number of applied or executed proposals.
To calculate the write success rate:
rate(etcd_server_proposals_applied_total[5m]) / rate(etcd_server_proposals_committed_total[5m])
etcd_server_proposals_pending
Gauge
The number of pending proposals.
To detect the stacked writes:
Counter
The number of failed proposals.
The kubelet-cadvisor-master component collects cAdvisor metrics from the master node's kubelet and exposes only the kube-apiserver container metrics.
Metric
Type
Example PromQL
Gauge
Cumulative CPU time consumed by a container, in seconds
CPU utilization of the kube-apiserver container:
sum by (cluster_name, pod) (rate(container_cpu_usage_seconds_total{container="kube-apiserver", cpu="total"}[5m])) / sum by (cluster_name, pod) ((container_spec_cpu_quota{container="kube-apiserver"} > 0) / 100000)
Gauge
CPU quota of a container
CPU quota of the kube-apiserver container:
container_spec_cpu_quota{container="kube-apiserver"}/100000
Gauge
Memory used by a container
Memory utilization of the kube-apiserver container:
container_memory_working_set_bytes{container="kube-apiserver"} / container_spec_memory_limit_bytes{container="kube-apiserver"}
Gauge
Memory limit for a container
Memory limit of the kube-apiserver container:
Helpful Link
For more information about Kubernetes system component metrics, see Kubernetes Metrics Reference.