Configuring Alarm Thresholds for an MRS Cluster
During MRS cluster O&M, administrators must monitor the running status of each node and service in the cluster in real time. When an exception occurs, such as high CPU usage, insufficient disk space, or service memory overflow, an alarm notification must be sent promptly for quick handling. By configuring alarm thresholds, administrators can set trigger conditions for each monitoring metric. When a metric value meets the preset conditions, the system automatically triggers an alarm and displays it on the alarm page, helping administrators detect and resolve issues early. This section describes how to configure alarm thresholds for an MRS cluster and lists the default thresholds for each monitoring metric.
Configuring Alarm Thresholds for a Cluster (MRS 3.x)
- Log in to FusionInsight Manager of the MRS cluster.
For details about how to log in to FusionInsight Manager, see Accessing MRS Manager.
- Choose O&M > Alarm > Thresholds.
- Select a monitoring metric for a host or service in the cluster. Figure 1 Configuring the threshold for a metric
For example, after selecting Host Memory Usage, the information about this indicator threshold is displayed.- If the alarm sending switch is turned on, an alarm will be triggered if the threshold is reached.
- When Alarm Severity is on, hierarchical alarms are enabled. The system dynamically reports alarms at each severity based on the real-time metric values and hierarchical thresholds set for the severity. MRS 3.3.0 or later supports this function.
- Alarm ID and Alarm Name: alarm information triggered against the threshold
- Trigger Count: MRS Manager checks whether a metric value reaches the threshold. If it reaches the threshold for the specified number of consecutive checks, the system generates an alarm. You can configure this trigger count.
- Check Period (s): interval for the system to check the monitoring metric.
- The rules in the rule list are used to trigger alarms.
- Click Create Rule to add rules used for monitoring indicators.
Table 1 Monitoring indicator rule parameters Parameter
Description
Example Value
Rule Name
Specifies the alarm rule name.
CPU_MAX
Alarm Severity
Select an alarm severity. After Alarm Severity is on, you need to configure the alarm severity in Thresholds. The alarm severity can be one of the following:
- Critical: Indicates a severe fault or issue within the system that could impact cluster running or lead to data loss. This severity level applies to extreme conditions, such as disk or memory usage exceeding 95%.
- Major: Indicates a significant impact on system performance or availability that requires prompt attention to prevent further degradation.
- Minor: Indicates small issues within the system that have no impact on overall system running. Alarms of this severity level should be monitored and addressed, but they have a low handling priority.
- Warning: Indicates the occurrence of a system event and serves purely as an informational notice or prompt.
Major
Threshold Type
You can use the maximum or minimum value of an indicator as the alarm triggering threshold. If Threshold Type is set to Max value, the system generates an alarm when the value of the specified indicator is greater than the threshold. If Threshold Type is set to Min value, the system generates an alarm when the value of the specified indicator is less than the threshold.
Max value
Date
This parameter is used to set the date when the rule takes effect. Possible values are as follows:
- Daily
- Weekly
- Others
If Alarm Severity is on, only Daily is supported.
Daily
Add Date
This parameter is available only when Date is set to Others. You can set the date when the rule takes effect. Multiple options are available.
09-30
Thresholds
This parameter is used to set the time range when the rule takes effect.
If Alarm Severity is on, you cannot set the start time and end time. The default start time and end time are 00:00-23:59.
Start and End Time: 00:00–08:30
Thresholds of the rule monitoring metric
After Alarm Severity is on, different alarm severities can be set for a cluster based on different thresholds.
You can click
to set multiple time ranges for the threshold or click
to delete one.Threshold: 10
- Click OK to save the rules.
- In the row of the target rule, click Apply in the Operation column.
A new rule can be applied only after you click Cancel for an existing rule.
On the Thresholds page, check whether Effective for the new rule is set to Yes. You can also check whether the alarm is generated or cleared as expected on the O&M > Alarms page.
Configuring Alarm Thresholds for a Cluster (Versions Earlier Than MRS 3.x)
- Log in to FusionInsight Manager of the MRS cluster.
For details about how to log in to FusionInsight Manager, see Accessing MRS Manager.
- Click System.
- In Configuration, click Configure Alarm Threshold under Monitoring and Alarm, select monitoring metrics as planned, and set their baselines.
- Click a metric, for example, CPU Usage, and click Create Rule.
- In the displayed dialog box, set monitoring metric rule parameters.
Table 2 Monitoring indicator rule parameters Parameter
Description
Example Value
Rule Name
Specifies the alarm rule name.
CPU_MAX
Reference Date
Specifies the date on which the reference indicator history is generated.
2014/11/06
Threshold Type
You can use the maximum or minimum value of an indicator as the alarm triggering threshold. If Threshold Type is set to Max value, the system generates an alarm when the value of the specified indicator is greater than the threshold. If Threshold Type is set to Min value, the system generates an alarm when the value of the specified indicator is less than the threshold.
Max value
Alarm Severity
Alarm severity. The value can be:
- Critical: Indicates a severe fault or issue within the system that could impact cluster running or lead to data loss.
- Major: Indicates a significant impact on system performance or availability that requires prompt attention to prevent further degradation.
- Minor: Indicates small issues within the system that have no impact on overall system running. Alarms of this severity level should be monitored and addressed, but they have a low handling priority.
- Warning: Indicates the occurrence of a system event and serves purely as an informational notice or prompt.
Major
Time Range
Specifies the period in which the rule takes effect.
From 00:00 to 23:59
Threshold
Specifies the threshold of the rule monitoring metrics.
80
Date
Date when the rule takes effect.
- Workday
- Weekend
- Other
Workday
Add Date
This parameter is valid only when Date is set to Other. You can select multiple dates.
11/30
- Click OK. A message is displayed in the upper right corner of the page, indicating that the template is saved successfully.
Send alarm is selected by default. Trigger Count: MRS Manager checks whether a metric value reaches the threshold. If it reaches the threshold for the specified number of consecutive checks, the system generates an alarm. You can configure this trigger count. Check Period (s) indicates the interval at which MRS Manager checks monitoring metrics.
- Locate the row that contains the newly added rule, and click Apply in the Operation column. A message is displayed in the upper right corner, indicating that the rule xx is successfully applied. Click Cancel in the Operation column. A message is displayed in the upper right corner, indicating that the rule xx is successfully canceled.
On the Thresholds page, verify that Cancel is displayed in the Operation column for the newly added rule (indicating that the rule has been applied). On the Alarms page, verify whether the alarm is generated or cleared as expected.
Threshold Alarm Metric Reference
FusionInsight Manager alarm monitoring metrics are classified as node information metrics and cluster service metrics. Table 3 lists the metrics whose thresholds can be configured for a node, and Table 4 lists the metrics whose thresholds can be configured for a component.
On FusionInsight Manager of MRS 3.3.0 or later, alarms of some components can be reported by severity. Each alarm severity has a threshold. You can view them on the FusionInsight Manager configuration page.
| Metric Group | Metric | Description | Default Threshold |
|---|---|---|---|
| CPU | Host CPU Usage | This indicator reflects the computing and control capabilities of the current cluster in a measurement period. By observing the indicator value, you can better understand the overall resource usage of the cluster. | 90.0% |
| Disk | Disk Usage | Indicates the disk usage of a host. | 90.0% |
| Disk Inode Usage | Indicates the disk inode usage in a measurement period. | 80.0% | |
| Memory | Host Memory Usage | Indicates the average memory usage at the current time. | 90.0% |
| Host Status | Host File Handle Usage | Indicates the usage of file handles of the host in a measurement period. | 80.0% |
| Host PID Usage | Indicates the PID usage of a host. | 90% | |
| Network Status | TCP Ephemeral Port Usage | Indicates the usage of temporary TCP ports of the host in a measurement period. | 80.0% |
| Network Reading | Read Packet Error Rate | Indicates the read packet error rate of the network interface on the host in a measurement period. | 0.5% |
| Read Packet Dropped Rate | Indicates the read packet dropped rate of the network interface on the host in a measurement period. | 0.5% | |
| Read Throughput Rate | Indicates the average read throughput (at MAC layer) of the network interface in a measurement period. | 80% | |
| Network Writing | Write Packet Error Rate | Indicates the write packet error rate of the network interface on the host in a measurement period. | 0.5% |
| Write Packet Dropped Rate | Indicates the write packet dropped rate of the network interface on the host in a measurement period. | 0.5% | |
| Write Throughput Rate | Indicates the average write throughput (at MAC layer) of the network interface in a measurement period. | 80% | |
| Process | Uninterruptible Sleep Process | Number of D state processes on the host in a measurement period | 0 |
| omm Process Usage | omm process usage in a measurement period | 90 |
| Service | Metric Group | Metric Name | Metric Description | Default Threshold |
|---|---|---|---|---|
| DBService | Database | Usage of the Number of Database Connections | Usage of database connections | 90% |
| Disk Space Usage of the Data Directory | Disk space usage of the data directory | 80% | ||
| Flume | Agent | Heap Memory Usage Calculate | Flume heap memory usage | 95.0% |
| Flume Direct Memory Usage Statistics | Flume direct memory usage | 80.0% | ||
| Flume Non-heap Memory Usage | Flume non-heap memory usage | 80.0% | ||
| Total GC duration of Flume process | Flume total GC time | 12000 ms | ||
| HBase | GC | GC time for old generation | Total GC time of RegionServer | 5000 ms |
| GC time for old generation | Total GC time of HMaster | 5000 ms | ||
| CPU & memory | RegionServer Direct Memory Usage Statistics | RegionServer direct memory usage | 90% | |
| RegionServer Heap Memory Usage Statistics | RegionServer heap memory usage | 90% | ||
| HMaster Direct Memory Usage | HMaster direct memory usage | 90% | ||
| HMaster Heap Memory Usage Statistics | HMaster heap memory usage | 90% | ||
| Service | Number of Online Regions of a RegionServer | Number of regions of a RegionServer | 2000 | |
| Region in transaction count over threshold | Number of regions that are in the RIT state and reach the threshold duration | 1 | ||
| Replication | Replication sync failed times (RegionServer) | Number of times that DR data fails to be synchronized | 1 | |
| Number of Log Files to Be Synchronized in the Active Cluster | Number of log files to be synchronized in the active cluster | 128 | ||
| Number of HFiles to Be Synchronized in the Active Cluster | Number of HFiles to be synchronized in the active cluster | 128 | ||
| Queue | Compaction Queue Size | Size of the Compaction queue | 100 | |
| HDFS | File and Block | Lost Blocks | Number of missing block replicas in HDFS | 0 |
| Blocks Under Replicated | Total number of blocks that need to be replicated by the NameNode | 1000 | ||
| RPC | Average Time of Active NameNode RPC Processing | Average NameNode RPC processing time | 100 ms | |
| Average Time of Active NameNode RPC Queuing | Average NameNode RPC queuing time | 200 ms | ||
| Disk | HDFS Disk Usage | HDFS disk usage | 80% | |
| DataNode Disk Usage | Disk usage of DataNodes in the HDFS | 80% | ||
| Percentage of Reserved Space for Replicas of Unused Space | Percentage of the reserved disk space of all the copies to the total unused disk space of DataNodes. | 90% | ||
| Resource | Faulty DataNodes | Indicates the number of faulty DataNodes. | 3 | |
| NameNode Non-Heap Memory Usage Statistics | Indicates the non-heap memory usage percentage of the NameNode. | 90% | ||
| NameNode Direct Memory Usage Statistics | Indicates the percentage of direct memory used by NameNodes. | 90% | ||
| NameNode Heap Memory Usage Statistics | Indicates the percentage of NameNode non-heap memory usage. | 95% | ||
| DataNode Direct Memory Usage Statistics | Indicates the percentage of direct memory used by DataNodes. | 90% | ||
| DataNode Heap Memory Usage Statistics | DataNode heap memory usage | 95% | ||
| DataNode Heap Memory Usage Statistics | Indicates the percentage of DataNode non-heap memory usage. | 90% | ||
| Garbage Collection | GC Time (NameNode)/GC Time (DataNode) | Indicates the Garbage collection (GC) duration of NameNodes per minute. | 12000 ms | |
| GC Time | Indicates the GC duration of DataNodes per minute. | 12000 ms | ||
| Hive | HQL | Percentage of HQL Statements That Are Executed Successfully by Hive | Indicates the percentage of HQL statements that are executed successfully by Hive. | 90.0% |
| Background | Background Thread Usage | Background thread usage | 90% | |
| GC | Total GC time of MetaStore | Indicates the total GC time of MetaStore. | 12000 ms | |
| Total GC Time in Milliseconds | Indicates the total GC time of HiveServer. | 12000 ms | ||
| Capacity | Percentage of HDFS Space Used by Hive to the Available Space | Indicates the percentage of HDFS space used by Hive to the available space. | 85.0% | |
| CPU & memory | MetaStore Direct Memory Usage Statistics | MetaStore direct memory usage | 95% | |
| MetaStore Non-Heap Memory Usage Statistics | MetaStore non-heap memory usage | 95% | ||
| MetaStore Heap Memory Usage Statistics | MetaStore heap memory usage | 95% | ||
| HiveServer Direct Memory Usage Statistics | HiveServer direct memory usage | 95% | ||
| HiveServer Non-Heap Memory Usage Statistics | HiveServer non-heap memory usage | 95% | ||
| HiveServer Heap Memory Usage Statistics | HiveServer heap memory usage | 95% | ||
| Session | Percentage of Sessions Connected to the HiveServer to Maximum Number of Sessions Allowed by the HiveServer | Indicates the percentage of the number of sessions connected to the HiveServer to the maximum number of sessions allowed by the HiveServer. | 90.0% | |
| Kafka | Partition | Percentage of Partitions That Are Not Completely Synchronized | Indicates the percentage of partitions that are not completely synchronized to total partitions. | 50% |
| Others | Unavailable Partition Percentage | Percentage of unavailable partitions of each Kafka topic | 40% | |
| User Connection Usage on Broker | Usage of user connections on Broker | 80% | ||
| Disk | Broker Disk Usage | Indicates the disk usage of the disk where the Broker data directory is located. | 80.0% | |
| Disk I/O Rate of a Broker | I/O usage of the disk where the Broker data directory is located | 80% | ||
| Process | Broker GC Duration per Minute | Indicates the GC duration of the Broker process per minute. | 12000 ms | |
| Heap Memory Usage of Kafka | Indicates the Kafka heap memory usage. | 95% | ||
| Kafka Direct Memory Usage | Indicates the Kafka direct memory usage. | 95% | ||
| Loader | Memory | Heap Memory Usage Calculate | Indicates the Loader heap memory usage. | 95% |
| Direct Memory Usage of Loader | Indicates the Loader direct memory usage. | 80.0% | ||
| Non-heap Memory Usage of Loader | Indicates the Loader non-heap memory usage. | 80% | ||
| GC | Total GC time of Loader | Indicates the total GC time of Loader. | 12000 ms | |
| MapReduce | Garbage Collection | GC Time | Indicates the GC time. | 12000 ms |
| Resource | JobHistoryServer Direct Memory Usage Statistics | Indicates the JobHistoryServer direct memory usage. | 90% | |
| JobHistoryServer Non-Heap Memory Usage Statistics | Indicates the JobHistoryServer non-heap memory usage. | 90% | ||
| JobHistoryServer Heap Memory Usage Statistics | Indicates the JobHistoryServer non-heap memory usage. | 95% | ||
| Oozie | Memory | Oozie Heap Memory Usage Calculate | Indicates the Oozie heap memory usage. | 95.0% |
| Oozie Direct Memory Usage | Indicates the Oozie direct memory usage. | 80.0% | ||
| Oozie Non-heap Memory Usage | Indicates the Oozie non-heap memory usage. | 80% | ||
| GC | Total GC duration of Oozie | Indicates the Oozie total GC time. | 12000 ms | |
| Spark/Spark2x | Memory | JDBCServer2x Heap Memory Usage Statistics | JDBCServer2x heap memory usage | 95% |
| JDBCServer2x Direct Memory Usage Statistics | JDBCServer2x direct memory usage | 95% | ||
| JDBCServer2x Non-Heap Memory Usage Statistics | JDBCServer2x non-heap memory usage | 95% | ||
| JobHistory2x Direct Memory Usage Statistics | JobHistory2x direct memory usage | 95% | ||
| JobHistory2x Non-Heap Memory Usage Statistics | JobHistory2x non-heap memory usage | 95% | ||
| JobHistory2x Heap Memory Usage Statistics | JobHistory2x heap memory usage | 95% | ||
| IndexServer2x Direct Memory Usage Statistics | IndexServer2x direct memory usage | 95% | ||
| IndexServer2x Heap Memory Usage Statistics | IndexServer2x heap memory usage | 95% | ||
| IndexServer2x Non-Heap Memory Usage Statistics | IndexServer2x non-heap memory usage | 95% | ||
| GC Count | Full GC Number of JDBCServer2x | Full GC times of JDBCServer2x | 12 | |
| Full GC Number of JobHistory2x | Full GC times of JobHistory2x | 12 | ||
| Full GC Number of IndexServer2x | Full GC times of IndexServer2x | 12 | ||
| GC Time | Total GC Time in Milliseconds | Total GC time of JDBCServer2x | 12000 ms | |
| Total GC Time in Milliseconds | Total GC time of JobHistory2x | 12000 ms | ||
| Total GC Time in Milliseconds | Total GC time of IndexServer2x | 12000 ms | ||
| Storm | Cluster | Number of Available Supervisors | Indicates the number of available Supervisor processes in the cluster in a measurement period. | 1 |
| Slot Usage | Indicates the slot usage in the cluster in a measurement period. | 80.0% | ||
| Nimbus | Nimbus Heap Memory Usage Calculate | Indicates the Nimbus heap memory usage. | 80% | |
| Yarn | Resources | NodeManager Direct Memory Usage Statistics | Indicates the percentage of direct memory used by NodeManagers. | 90% |
| NodeManager Heap Memory Usage Statistics | Indicates the percentage of NodeManager heap memory usage. | 95% | ||
| NodeManager Non-Heap Memory Usage Statistics | Indicates the percentage of NodeManager non-heap memory usage. | 90% | ||
| ResourceManager Direct Memory Usage Statistics | Indicates the ResourceManager direct memory usage. | 90% | ||
| ResourceManager Heap Memory Usage Statistics | Indicates the ResourceManager heap memory usage. | 95% | ||
| ResourceManager Non-Heap Memory Usage Statistics | Indicates the ResourceManager non-heap memory usage. | 90% | ||
| Garbage collection | GC Time | Indicates the GC duration of NodeManager per minute. | 12000 ms | |
| GC Time | Indicates the GC duration of ResourceManager per minute. | 12000 ms | ||
| Others | Failed Applications of root queue | Number of failed tasks in the root queue | 50 | |
| Terminated Applications of root queue | Number of killed tasks in the root queue | 50 | ||
| CPU & memory | Pending Memory | Pending memory capacity | 83886080 MB | |
| Application | Pending Applications | Pending tasks | 60 | |
| ZooKeeper | Connection | ZooKeeper Connections Usage | Indicates the percentage of the used connections to the total connections of ZooKeeper. | 80% |
| CPU & memory | Heap Memory Usage | Indicates the ZooKeeper heap memory usage. | 95% | |
| Heap Memory Usage Calculate | Indicates the ZooKeeper direct memory usage. | 80% | ||
| GC | ZooKeeper GC Duration per Minute | Indicates the GC time of ZooKeeper every minute. | 12000 ms | |
| Ranger | GC | UserSync GC Duration | UserSync garbage collection (GC) duration | 12000 ms |
| RangerAdmin GC Duration | RangerAdmin GC duration | 12000 ms | ||
| TagSync GC Duration | TagSync GC duration | 12000 ms | ||
| CPU & memory | UserSync Non-Heap Memory Usage | UserSync non-heap memory usage | 80.0% | |
| UserSync Direct Memory Usage | UserSync direct memory usage | 80.0% | ||
| UserSync Heap Memory Usage | UserSync heap memory usage | 95.0% | ||
| RangerAdmin Non-Heap Memory Usage | RangerAdmin non-heap memory usage | 80.0% | ||
| RangerAdmin Heap Memory Usage | RangerAdmin heap memory usage | 95.0% | ||
| RangerAdmin Direct Memory Usage | RangerAdmin direct memory usage | 80.0% | ||
| TagSync Direct Memory Usage | TagSync direct memory usage | 80.0% | ||
| TagSync Non-Heap Memory Usage | TagSync non-heap memory usage | 80.0% | ||
| TagSync Heap Memory Usage | TagSync heap memory usage | 95.0% | ||
| ClickHouse | Cluster Quota | Quota of the ZooKeeper Nodes Used by a ClickHouse Service | Quota of the ZooKeeper nodes used by a ClickHouse service. | 90% |
| Capacity Quota of ZooKeeper Used by a ClickHouse Service | Capacity quota of ZooKeeper directory used by the ClickHouse service | 90% | ||
| IoTDB | GC | IoTDBServer GC Duration | IoTDBServer garbage collection (GC) duration | 12000 ms |
| CPU & memory | IoTDBServer Heap Memory Usage | IoTDBServer heap memory usage | 90% | |
| IoTDBServer Direct Memory Usage | IoTDBServer direct memory usage | 90% |
Verifying the configuration:
- After saving and applying the rule, verify that Effective for the rule is set to Yes.
- Choose O&M > Alarm > Alarms and verify that alarm information for the corresponding metric is received.
- To verify that alarms trigger properly, temporarily set a threshold below the current metric value and confirm that the corresponding alarm appears in the alarm list.
FAQs
- What should I do if no alarm is generated after I configure an alarm threshold?
Ensure that Effective for the rule is set to Yes and that the alarm function is enabled. Verify that Trigger Count is configured correctly (a value that is too high can delay alarm generation), and ensure that the actual metric value exceeds the threshold for the number of times specified by the Trigger Count.
- What are the differences between hierarchical alarms and common alarms?
Common alarms support only a single threshold and alarm severity. Hierarchical alarms allow you to set multiple alarm severities based on different threshold levels. For example, a Minor alarm is generated when CPU usage exceeds 80%, and a Critical alarm is generated when CPU usage exceeds 95%. This enables more refined alarm management.
- How do I set appropriate alarm thresholds?
You are advised to configure thresholds based on the default values provided in this section. For key resource metrics, such as disk usage and memory usage, set the threshold between 90% and 95%. For fault tolerance metrics, such as the number of missing HDFS blocks, set the threshold to 0. Adjust these thresholds based on your actual service load and cluster scale.
Helpful Links
- For details about how to log in to MRS Manager, see Accessing MRS Manager.
- For details about how to view cluster node resource monitoring metrics, see Viewing MRS Node Resource Monitoring Metrics.