Configuring the Threshold
Updated on 2024-10-11 GMT+08:00
You can configure monitoring indicator thresholds to monitor the health status of indicators on FusionInsight Manager. If abnormal data occurs and the preset conditions are met, the system triggers an alarm and displays the alarm information on the alarm page.
  2. Choose O&M > Alarm > Thresholds.
  3. Select a monitoring metric for a host or service in the cluster.
    Figure 1 Configuring the threshold for a metric
    For example, after selecting Host Memory Usage, the information about this indicator threshold is displayed.
    • If the alarm sending switch is displayed as , an alarm is triggered if the threshold is reached.
    • Alarm ID and Alarm Name: alarm information triggered against the threshold
    • Trigger Count: FusionInsight Manager checks whether the value of a monitoring metric reaches the threshold. If the number of consecutive checks reaches the value of Trigger Count, an alarm is generated. Trigger Count is configurable.
    • Check Period (s): interval for the system to check the monitoring metric.
    • The rules in the rule list are used to trigger alarms.
  4. Click Create Rule to add rules used for monitoring indicators.
    Table 1 Monitoring indicator rule parameters
    Example Value
    Rule Name
    Name of a rule.
    CPU_MAX
    Severity
    Alarm Severity
    • Critical
    • Major
    • Minor
    • Warning
    • Critical
    • Major
    • Minor
    • Warning
    Threshold Type
    You can use the maximum or minimum value of an indicator as the alarm triggering threshold. If Threshold Type is set to Max value, the system generates an alarm when the value of the specified indicator is greater than the threshold. If Threshold Type is set to Min value, the system generates an alarm when the value of the specified indicator is less than the threshold.
    • Max value
    • Min value
    Date
    This parameter is used to set the date when the rule takes effect.
    • Daily
    • Weekly
    • Others
    Add Date
    This parameter is available only when Date is set to Others. You can set the date when the rule takes effect. Multiple options are available.
    09-30
    Thresholds
    This parameter is used to set the time range when the rule takes effect.
    Start and End Time: 00:00–08:30
    Threshold of the rule monitoring metric
    Threshold: 10
    You can click or to add or delete time thresholds.
  5. Click OK to save the rules.
  6. Locate the row that contains an added rule, and click Apply in the Operation column. The value of Effective for this rule changes to Yes.
    A new rule can be applied only after you click Cancel for an existing rule.
Monitoring Metric Reference
FusionInsight Manager alarm monitoring metrics are classified as node information metrics and cluster service metrics. Table 2 describes the metrics for which you can configure thresholds on nodes.
Table 2 Node monitoring metrics
Metric Group
Metric
Default Threshold
CPU
Host CPU Usage
This indicator reflects the computing and control capabilities of the current cluster in a measurement period. By observing the indicator value, you can better understand the overall resource usage of the cluster.
90.0%
Disk
Disk Usage
Indicates the disk usage of a host.
90.0%
Disk Inode Usage
Indicates the disk inode usage in a measurement period.
80.0%
Memory
Host Memory Usage
Indicates the average memory usage at the current time.
90.0%
Host Status
Host File Handle Usage
Indicates the usage of file handles of the host in a measurement period.
80.0%
Host PID Usage
Indicates the PID usage of a host.
90%
Network Status
TCP Ephemeral Port Usage
Indicates the usage of temporary TCP ports of the host in a measurement period.
80.0%
Network Reading
Read Packet Error Rate
Indicates the read packet error rate of the network interface on the host in a measurement period.
0.5%
Read Packet Dropped Rate
Indicates the read packet dropped rate of the network interface on the host in a measurement period.
0.5%
Read Throughput Rate
Indicates the average read throughput (at MAC layer) of the network interface in a measurement period.
80%
Network Writing
Write Packet Error Rate
Indicates the write packet error rate of the network interface on the host in a measurement period.
0.5%
Write Packet Dropped Rate
Indicates the write packet dropped rate of the network interface on the host in a measurement period.
0.5%
Write Throughput Rate
Indicates the average write throughput (at MAC layer) of the network interface in a measurement period.
80%
Process
Uninterruptible Sleep Process
Number of D state processes on the host in a measurement period
0
omm Process Usage
omm process usage in a measurement period
90
Table 3 Cluster service indicators
Service
Monitoring Indicator Group Name
Indicator Name
Default Threshold
DBService
Database
Usage of the Number of Database Connections
Indicates the usage of the number of database connections.
90%
Disk Space Usage of the Data Directory
Disk space usage of the data directory
80%
Flume
Agent
Heap Memory Usage Calculate
Indicates the Flume heap memory usage.
95.0%
Flume Direct Memory Usage Statistics
Indicates the Flume direct memory usage.
80.0%
Flume Non-heap Memory Usage
Indicates the Flume non-heap memory usage.
80.0%
Total GC duration of Flume process
Indicates the Flume total GC time.
12000 ms
HBase
GC
GC time for old generation
Total GC time of RegionServer
5000 ms
Indicates he total GC time of HMaster.
5000 ms
CPU & memory
RegionServer Direct Memory Usage Statistics
Indicates theRegionServerReg direct memory usage.
90%
RegionServer Heap Memory Usage Statistics
Indicates the RegionServer heap memory usage.
90%
HMaster Direct Memory Usage
Indicates the HMaster direct memory usage.
90%
HMaster Heap Memory Usage Statistics
Indicates the HMaster heap memory usage.
90%
Service
Number of Online Regions of a RegionServer
Number of regions of a RegionServer
2000
Region in transaction count over threshold
Number of regions that are in the RIT state and reach the threshold duration
Replication
Replication sync failed times (RegionServer)
Indicates the number of times that DR data fails to be synchronized.
Number of Log Files to Be Synchronized in the Active Cluster
Number of log files to be synchronized in the active cluster
128
Number of HFiles to Be Synchronized in the Active Cluster
Number of HFiles to be synchronized in the active cluster
128
Queue
Compaction Queue Size
Size of the Compaction queue
100
HDFS
File and Block
Lost Blocks
Indicates the number of block copies that the HDFS lacks of.
0
Blocks Under Replicated
Total number of blocks that need to be replicated by the NameNode
1000
RPC
Average Time of Active NameNode RPC Processing
Indicates the average RPC processing time.
100 ms
Average Time of Active NameNode RPC Queuing
Indicates the average RPC queuing time.
200 ms
Disk
HDFS Disk Usage
Indicates the HDFS disk usage.
80%
DataNode Disk Usage
Indicates the disk usage of DataNodes in the HDFS.
80%
Percentage of Reserved Space for Replicas of Unused Space
Indicates the percentage of the reserved disk space of all the copies to the total unused disk space of DataNodes.
90%
Resource
Faulty DataNodes
Indicates the number of faulty DataNodes.
3
NameNode Non Heap Memory Usage Statistics
Indicates the percentage of NameNode non-heap memory usage.
90%
NameNode Direct Memory Usage Statistics
Indicates the percentage of direct memory used by NameNodes.
90%
NameNode Heap Memory Usage Statistics
95%
DataNode Direct Memory Usage Statistics
Indicates the percentage of direct memory used by DataNodes.
90%
DataNode Heap Memory Usage Statistics
DataNode heap memory usage
95%
Indicates the percentage of DataNode non-heap memory usage.
90%
Garbage Collection
GC Time (NameNode)/GC Time (DataNode)
Indicates the Garbage collection (GC) duration of NameNodes per minute.
12000 ms
GC Time
Indicates the GC duration of DataNodes per minute.
12000 ms
Hive
HQL
Percentage of HQL Statements That Are Executed Successfully by Hive
Indicates the percentage of HQL statements that are executed successfully by Hive.
90.0%
Background
Background Thread Usage
Background thread usage
90%
GC
Total GC time of MetaStore
Indicates the total GC time of MetaStore.
12000 ms
Total GC Time in Milliseconds
Indicates the total GC time of HiveServer.
12000 ms
Capacity
Percentage of HDFS Space Used by Hive to the Available Space
Indicates the percentage of HDFS space used by Hive to the available space.
85.0%
CPU & memory
MetaStore Direct Memory Usage Statistics
MetaStore direct memory usage
95%
MetaStore Non-Heap Memory Usage Statistics
MetaStore non-heap memory usage
95%
MetaStore Heap Memory Usage Statistics
MetaStore heap memory usage
95%
HiveServer Direct Memory Usage Statistics
HiveServer direct memory usage
95%
HiveServer Non-Heap Memory Usage Statistics
HiveServer non-heap memory usage
95%
HiveServer Heap Memory Usage Statistics
HiveServer heap memory usage
95%
Session
Percentage of Sessions Connected to the HiveServer to Maximum Number of Sessions Allowed by the HiveServer
Indicates the percentage of the number of sessions connected to the HiveServer to the maximum number of sessions allowed by the HiveServer.
90.0%
Kafka
Partition
Percentage of Partitions That Are Not Completely Synchronized
Indicates the percentage of partitions that are not completely synchronized to total partitions.
50%
Unavailable Partition Percentage
Percentage of unavailable partitions of each Kafka topic
40%
User Connection Usage on Broker
Usage of user connections on Broker
80%
Disk
Broker Disk Usage
Indicates the disk usage of the disk where the Broker data directory is located.
80.0%
Disk I/O Rate of a Broker
I/O usage of the disk where the Broker data directory is located
80%
Process
Broker GC Duration per Minute
Indicates the GC duration of the Broker process per minute.
12000 ms
Heap Memory Usage of Kafka
Indicates the Kafka heap memory usage.
95%
Kafka Direct Memory Usage
Indicates the Kafka direct memory usage.
95%
Loader
Memory
Indicates the Loader heap memory usage.
95%
Direct Memory Usage of Loader
Indicates the Loader direct memory usage.
80.0%
Non-heap Memory Usage of Loader
Indicates the Loader non-heap memory usage.
80%
GC
Total GC time of Loader
Indicates the total GC time of Loader.
12000 ms
MapReduce
Garbage Collection
GC Time
Indicates the GC time.
12000 ms
Resource
JobHistoryServer Direct Memory Usage Statistics
Indicates the JobHistoryServer direct memory usage.
90%
JobHistoryServer Non Heap Memory Usage Statistics
Indicates the JobHistoryServer non-heap memory usage.
90%
JobHistoryServer Heap Memory Usage Statistics
95%
Oozie
Memory
Indicates the Oozie heap memory usage.
95.0%
Oozie Direct Memory Usage
Indicates the Oozie direct memory usage.
80.0%
Oozie Non-heap Memory Usage
Indicates the Oozie non-heap memory usage.
80%
GC
Total GC duration of Oozie
Indicates the Oozie total GC time.
12000 ms
Spark2x
Memory
JDBCServer2x Heap Memory Usage Statistics
JDBCServer2x heap memory usage
95%
JDBCServer2x Direct Memory Usage Statistics
JDBCServer2x direct memory usage
95%
JDBCServer2x Non-Heap Memory Usage Statistics
JDBCServer2x non-heap memory usage
95%
JobHistory2x Direct Memory Usage Statistics
JobHistory2x direct memory usage
95%
JobHistory2x Non-Heap Memory Usage Statistics
JobHistory2x non-heap memory usage
95%
JobHistory2x Heap Memory Usage Statistics
JobHistory2x heap memory usage
95%
IndexServer2x Direct Memory Usage Statistics
IndexServer2x direct memory usage
95%
IndexServer2x Heap Memory Usage Statistics
IndexServer2x heap memory usage
95%
IndexServer2x Non-Heap Memory Usage Statistics
IndexServer2x non-heap memory usage
95%
GC Count
Full GC Number of JDBCServer2x
Total GC number of JDBCServer2x
12
Full GC Number of JobHistory2x
Total GC number of JobHistory2x
12
Full GC Number of IndexServer2x
Total GC number of IndexServer2x
12
GC Time
Total GC time of JDBCServer2x
12000 ms
Total GC time of JobHistory2x
12000 ms
Total GC time of IndexServer2x
12000 ms
Storm
Cluster
Number of Available Supervisors
Indicates the number of available Supervisor processes in the cluster in a measurement period.
Slot Usage
Indicates the slot usage in the cluster in a measurement period.
80.0%
Nimbus
Indicates the Nimbus heap memory usage.
80%
Yarn
Resources
NodeManager Direct Memory Usage Statistics
Indicates the percentage of direct memory used by NodeManagers.
90%
NodeManager Heap Memory Usage Statistics
Indicates the percentage of NodeManager heap memory usage.
95%
NodeManager Non Heap Memory Usage Statistics
Indicates the percentage of NodeManager non-heap memory usage.
90%
ResourceManager Direct Memory Usage Statistics
90%
ResourceManager Heap Memory Usage Statistics
Indicates the ResourceManager heap memory usage.
95%
ResourceManager Non Heap Memory Usage Statistics
Indicates the ResourceManager non-heap memory usage.
90%
Garbage collection
GC Time
Indicates the GC duration of NodeManager per minute.
12000 ms
GC Time
Indicates the GC duration of ResourceManager per minute.
12000 ms
Failed Applications of root queue
Number of failed tasks in the root queue
50
Terminated Applications of root queue
Number of killed tasks in the root queue
50
CPU & memory
Pending Memory
Pending memory capacity
83886080MB
Application
Pending Applications
Pending tasks
60
ZooKeeper
Connection
ZooKeeper Connections Usage
Indicates the percentage of the used connections to the total connections of ZooKeeper.
80%
CPU & memory
Directmemory Usage Calculate
Indicates the ZooKeeper heap memory usage.
95%
Indicates the ZooKeeper direct memory usage.
80%
GC
ZooKeeper GC Duration per Minute
Indicates the GC time of ZooKeeper every minute.
12000 ms
meta
OBS data write operation
Success Rate for Calling the OBS Write API
Success rate for calling the OBS data read API
99.0%
OBS Meta data Operations
Average Time for Calling the OBS Metadata API
Average time for calling the OBS metadata API
500ms
Success Rate for Calling the OBS Metadata API
Success rate for calling the OBS metadata API
99.0%
OBS data read operation
Success Rate for Calling the OBS Data Read API
99.0%
Ranger
GC
UserSync GC Duration
UserSync garbage collection (GC) duration
12000 ms
RangerAdmin GC Duration
RangerAdmin GC duration
12000 ms
TagSync GC Duration
TagSync GC duration
12000 ms
CPU & memory
UserSync Non-Heap Memory Usage
UserSync non-heap memory usage
80.0%
UserSync Direct Memory Usage
UserSync direct memory usage
80.0%
UserSync Heap Memory Usage
UserSync heap memory usage
95.0%
RangerAdmin Non-Heap Memory Usage
RangerAdmin non-heap memory usage
80.0%
RangerAdmin Heap Memory Usage
RangerAdmin heap memory usage
95.0%
RangerAdmin Direct Memory Usage
RangerAdmin direct memory usage
80.0%
TagSync Direct Memory Usage
TagSync direct memory usage
80.0%
TagSync Non-Heap Memory Usage
TagSync non-heap memory usage
80.0%
TagSync Heap Memory Usage
TagSync heap memory usage
95.0%
ClickHouse
Cluster Quota
Clickhouse service quantity quota usage in ZooKeeper
Quota of the ZooKeeper nodes used by a ClickHouse service
90%
Capacity quota usage of the Clickhouse service in ZooKeeper
Capacity quota of ZooKeeper directory used by the ClickHouse service
90%
