ALM-14015 DataNode GC Time Exceeds the Threshold
Description
The system checks the garbage collection (GC) duration of the DataNode process every 60 seconds. This alarm is generated when the GC duration exceeds the threshold.
This alarm is cleared when the GC duration is less than the threshold.
Attribute
| Alarm ID | Alarm Severity | Automatically Cleared |
|---|---|---|
| 14015 | Critical (default threshold: 20000ms) Major (default threshold: 12000ms) | Yes |
Parameters
| Name | Meaning |
|---|---|
| Source | Specifies the cluster for which the alarm is generated. |
| ServiceName | Specifies the service for which the alarm is generated. |
| RoleName | Specifies the role for which the alarm is generated. |
| HostName | Specifies the host for which the alarm is generated. |
| Trigger Condition | Specifies the threshold triggering the alarm. If the current indicator value exceeds this threshold, the alarm is generated. |
Impact on the System
A long GC duration of the DataNode process may interrupt the services and users cannot read or write files.
Possible Causes
The heap memory of the DataNode instance is overused or the heap memory is inappropriately allocated. As a result, GCs occur frequently.
Procedure
Check the GC duration.
- On the FusionInsight Manager portal, choose O&M > Alarm > Alarms. On the displayed interface, click the drop-down button of ALM-14015 DataNode GC Time Exceeds the Threshold. Then check the role name in Location and confirm the IP address of the instance.
- On the Home page of FusionInsight Manager, choose Cluster > Name of the target cluster > Services > HDFS. On the page that is displayed, click the Instance tab. In the instance list, select DataNode (IP address of the instance for which this alarm is generated). Click the drop-down list in the upper right corner of the chart area, choose Customize > Garbage Collection, and select DataNode Garbage Collection (GC). Check the GC duration statistics of the DataNode process every minute. Figure 1 DataNode Garbage Collection (GC)
- Check whether the GC duration of the DataNode process collected every minute exceeds the threshold (12 seconds by default).
- On FusionInsight Manager, choose Cluster, click the name of the desired cluster, and choose Services > HDFS > Configurations > All Configurations > DataNode > System. Increase the value of the GC_OPTS parameter as required.
The mapping between the average number of blocks of a DataNode instance and the DataNode memory is as follows:
- If the average number of blocks of a DataNode instance reaches 2,000,000, the reference values of the JVM parameters of the DataNode are as follows: -Xms6G -Xmx6G -XX:NewSize=512M -XX:MaxNewSize=512M
- If the average number of blocks of a DataNode instance reaches 5,000,000, the reference values of the JVM parameters of the DataNode are as follows: -Xms12G -Xmx12G -XX:NewSize=1G -XX:MaxNewSize=1G
- Save the configuration and restart the DataNode instance.
Services may be affected or interrupted during the restart. You are advised to perform this operation during off-peak hours.
- Check whether the alarm is cleared.
- If yes, no further action is required.
- If no, go to Step 7.
Collect fault information.
- On the FusionInsight Manager portal, choose O&M > Log > Download.
- Select DataNode in the required cluster from the Service.
- Click
in the upper right corner, and set Start Date and End Date for log collection to 10 minutes ahead of and after the alarm generation time, respectively. Then, click Download. - Contact the O&M personnel and send the collected logs.
Alarm Clearing
After the fault is rectified, the system automatically clears this alarm.