Using Annotations to Balance Load
You can add annotations to a YAML file to use some CCE advanced functions. This section describes the available annotations when a LoadBalancer service is created.
Interconnection with ELB
Table 1 Annotations for interconnecting with ELB
Type
Supported Cluster Version
kubernetes.io/elb.class
String
Select a proper load balancer type.
The value can be:
  • union: shared load balancer
  • performance: dedicated load balancer, which can be used only in clusters of v1.17 and later.
v1.9 or later
kubernetes.io/elb.id
String
Mandatory when an existing load balancer is to be associated.
ID of a load balancer.
How to obtain:
On the management console, click Service List, and choose Networking > Elastic Load Balance. Click the name of the target load balancer. On the Summary tab page, find and copy the ID.
The system preferentially connects to the load balancer based on the kubernetes.io/elb.id field. If this field is not specified, the spec.loadBalancerIP field is used (optional and available only in 1.23 and earlier versions).
Do not use the spec.loadBalancerIP field to connect to the load balancer. This field will be discarded by Kubernetes. For details, see Deprecation.
v1.9 or later
kubernetes.io/elb.autocreate
Table 13
Mandatory when load balancers are automatically created.
Example:
  • If a public network load balancer will be automatically created, set this parameter to the following value:
    '{"type":"public","bandwidth_name":"cce-bandwidth-1551163379627","bandwidth_chargemode":"bandwidth","bandwidth_size":5,"bandwidth_sharetype":"PER","eip_type":"5_bgp","name":"james"}'
  • If a private network load balancer will be automatically created, set this parameter to the following value:
    {"type":"inner","name":"A-location-d-test"}
v1.9 or later
kubernetes.io/elb.subnet-id
String
Optional when load balancers are automatically created.
ID of the subnet where the cluster is located. The value can contain 1 to 100 characters.
  • Mandatory when a cluster of v1.11.7-r0 or earlier is to be automatically created.
  • Optional for clusters later than v1.11.7-r0.
Mandatory for clusters earlier than v1.11.7-r0
Discarded in clusters later than v1.11.7-r0
kubernetes.io/elb.lb-algorithm
String
Specifies the load balancing algorithm of the backend server group. The default value is ROUND_ROBIN.
Options:
  • ROUND_ROBIN: weighted round robin algorithm
  • LEAST_CONNECTIONS: weighted least connections algorithm
  • SOURCE_IP: source IP hash algorithm
If this parameter is set to SOURCE_IP, the weight setting (weight field) of backend servers bound to the backend server group is invalid, and sticky session cannot be enabled.
v1.9 or later
The following shows how to use the preceding annotations:
  • Associate an existing load balancer. For details, see Using kubectl to Create a Service (Using an Existing Load Balancer).
    apiVersion: v1
    kind: Service
      annotations:
        kubernetes.io/elb.id: <your_elb_id>                         # Load balancer ID. Replace it with the actual value.
        kubernetes.io/elb.class: performance                        # Load balancer type
        kubernetes.io/elb.lb-algorithm: ROUND_ROBIN                   # Load balancer algorithm
      selector:
         app: nginx
      ports:
      - name: service0
        port: 80
        protocol: TCP
        targetPort: 80
      type: LoadBalancer
  • Automatically create a load balancer. For details, see Using kubectl to Create a Service (Automatically Creating a Load Balancer).
    Shared load balancer:
    apiVersion: v1
    kind: Service
      annotations:
        kubernetes.io/elb.class: union
        kubernetes.io/elb.autocreate: '{
          "type": "public",
          "bandwidth_name": "cce-bandwidth-1551163379627",
          "bandwidth_chargemode": "bandwidth",
          "bandwidth_size": 5,
          "bandwidth_sharetype": "PER",
          "eip_type": "5_bgp"
      labels:
        app: nginx
      ports:
      - name: service0
        port: 80
        protocol: TCP
        targetPort: 80
      selector:
        app: nginx
      type: LoadBalancer
    Dedicated load balancer:
    apiVersion: v1
    kind: Service
      labels:
        app: nginx
      namespace: default
      annotations:
          "type": "public",
          "bandwidth_name": "cce-bandwidth-1626694478577",
          "eip_type": "5_bgp",
          "available_zone": [
          "l4_flavor_name": "L4_flavor.elb.s1.small"
      selector:
        app: nginx
      ports:
      - name: cce-service-0
        targetPort: 80
        nodePort: 0
        port: 80
        protocol: TCP
      type: LoadBalancer
Sticky Session
Table 2 Annotations for sticky session
Type
kubernetes.io/elb.session-affinity-mode
String
Source IP address-based sticky session means that access requests from the same IP address are forwarded to the same backend server.
  • Disabling sticky session: Do not configure this parameter.
  • Enabling sticky session: Set this parameter to SOURCE_IP, indicating that the sticky session is based on the source IP address.
When kubernetes.io/elb.lb-algorithm is set to SOURCE_IP (source IP hash), sticky session cannot be enabled.
v1.9 or later
kubernetes.io/elb.session-affinity-option
Table 16
Sticky session timeout.
v1.9 or later
apiVersion: v1
kind: Service
  annotations:
    kubernetes.io/elb.class: union                   # Load balancer type
    kubernetes.io/elb.session-affinity-mode: SOURCE_IP          # The sticky session type is source IP address.
    kubernetes.io/elb.session-affinity-option: '{"persistence_timeout": "30"}'     # Stickiness duration (min)
  selector:
     app: nginx
  ports:
  - name: service0
    port: 80
    protocol: TCP
    targetPort: 80
  type: LoadBalancer
Health Check
Table 3 Annotations for health check
Type
kubernetes.io/elb.health-check-flag
String
Whether to enable the ELB health check.
  • Enabling health check: Leave blank this parameter or set it to on.
  • Disabling health check: Set this parameter to off.
If this parameter is enabled, the kubernetes.io/elb.health-check-option field must also be specified at the same time.
v1.9 or later
Table 14
ELB health check configuration items.
v1.9 or later
kubernetes.io/elb.health-check-options
Table 15
ELB health check configuration items. Each Service port can be configured separately, and you can configure only some ports.
Either kubernetes.io/elb.health-check-option or kubernetes.io/elb.health-check-options can be configured.
v1.19.16-r5 or later
v1.21.8-r0 or later
v1.23.6-r0 or later
v1.25.2-r0 or later
  • The following shows how to use kubernetes.io/elb.health-check-option:
    apiVersion: v1
    kind: Service
      annotations:
        kubernetes.io/elb.health-check-flag: 'on'                   # Enable ELB health check.
        kubernetes.io/elb.health-check-option: '{
          "protocol":"TCP",
          "delay":"5",
          "timeout":"10",
          "max_retries":"3"
      selector:
         app: nginx
      ports:
      - name: service0
        port: 80
        protocol: TCP
        targetPort: 80
      type: LoadBalancer
  • For details about how to use kubernetes.io/elb.health-check-options, see Configuring Health Check on Multiple Ports of a LoadBalancer Service.
HTTP or HTTPS
Table 4 Annotations for using HTTP or HTTPS
Type
kubernetes.io/elb.protocol-port
String
If a Service is HTTP/HTTPS-compliant, configure the protocol and port number in the format of "protocol:port".
where,
  • protocol: specifies the protocol used by the listener port. The value can be http or https.
  • ports: Service ports specified by spec.ports[].port.
v1.19.16 or later
kubernetes.io/elb.cert-id
String
ID of an ELB certificate, which is used as the HTTPS server certificate.
To obtain the certificate, log in to the CCE console, choose Service List > Networking > Elastic Load Balance, and click Certificates in the navigation pane. In the load balancer list, copy the ID under the target certificate name.
v1.19.16 or later
For details, see Configuring HTTP/HTTPS for a LoadBalancer Service.
SNI
Table 5 Annotations for using SNIs
Type
kubernetes.io/elb.tls-certificate-ids
String
In ELB, the IDs of SNI certificates that must contain a domain name are separated by commas (,).
v1.23.13-r0, v1.25.8-r0, v1.27.5-r0, v1.28.3-r0, or later
HTTPS must be enabled. For details, see Configuring SNI for a LoadBalancer Service.
Dynamic Adjustment of the Weight of the Backend ECS
Table 6 Annotations for dynamically adjusting the weight of the backend ECS
Type
kubernetes.io/elb.adaptive-weight
String
Dynamically adjust the weight of the load balancer backend server based on the number pods on the server. In this way, the requests received by each pod are more balanced.
  • true: enabled
  • false: disabled
v1.21 or later
This parameter is invalid in passthrough networking, where dedicated load balancers are used in a CCE Turbo cluster.
apiVersion: v1
kind: Service
  annotations:
    kubernetes.io/elb.adaptive-weight: 'true'                   # Enable dynamic adjustment of the weight of the backend ECS.
  selector:
     app: nginx
  ports:
  - name: service0
    port: 80
    protocol: TCP
    targetPort: 80
  type: LoadBalancer
Passthrough Capability
Table 7 Annotations for passthrough capability
Type
kubernetes.io/elb.pass-through
String
Whether the access requests from within the cluster to the Service pass through the ELB load balancer.
v1.19 or later
For details, see Configuring Passthrough Networking for a LoadBalancer Service.
Blocklist/Trustlist
Table 8 Annotations for ELB access control
Type
kubernetes.io/elb.acl-id
String
  • If this parameter is not specified, CCE does not modify access control on the ELB.
  • If this parameter is left empty, all IP addresses are allowed to access the load balancer.
  • If this parameter is set to the IP address group ID of the load balancer, access control is enabled and you need to configure an IP address blocklist or trustlist for the load balancer. Additionally, you need to configure both kubernetes.io/elb.acl-status and kubernetes.io/elb.acl-type.
    How to obtain:
    Log in to the console. In the Service List, choose Networking > Elastic Load Balance. On the Network Console, choose Elastic Load Balance > IP Address Groups and copy the ID of the target IP address group.
v1.23.12-r0, v1.25.7-r0, v1.27.4-r0, v1.28.2-r0, or later
String
This parameter is mandatory when you configure an IP address blocklist or trustlist for a load balancer. Options:
  • on: Access control is enabled.
  • off: Access control is disabled.
String
  • black: indicates a blocklist. The selected IP address group cannot access the load balancer.
  • white: indicates a trustlist. Only the selected IP address group can access the load balancer.
apiVersion: v1
kind: Service
  annotations:
    kubernetes.io/elb.acl-id: <your_acl_id>               # ID of an IP address group for accessing a load balancer
    kubernetes.io/elb.acl-status: 'on'                    # Enable access control.
    kubernetes.io/elb.acl-type: 'white'                   # Trustlist for access control
  selector:
     app: nginx
  ports:
  - name: service0
    port: 80
    protocol: TCP
    targetPort: 80
  type: LoadBalancer
Host Network
Table 9 Annotations for host network
Type
kubernetes.io/hws-hostNetwork
String
If the pod uses hostNetwork, the ELB forwards the request to the host network after this annotation is used.
Options:
  • true: enabled
  • false (default): disabled
v1.9 or later
apiVersion: v1
kind: Service
  annotations:
    kubernetes.io/hws-hostNetwork: 'true'                     # The load balancer forwards the request to the host network.
  selector:
     app: nginx
  ports:
  - name: service0
    port: 80
    protocol: TCP
    targetPort: 80
  type: LoadBalancer
Timeout
Table 10 Annotation for configuring timeout
Type
kubernetes.io/elb.keepalive_timeout
String
Timeout for client connections. If there are no requests reaching the load balancer during the timeout duration, the load balancer will disconnect the connection from the client and establish a new connection when there is a new request.
Value:
  • For TCP listeners, the value ranges from 10 to 4000 (in seconds). The default value is 300.
  • For HTTP, HTTPS, and TERMINATED_HTTPS listeners, the value ranges from 0 to 4000 (in seconds). The default value is 60.
  • For UDP listeners, this parameter does not take effect.
Dedicated load balancers: v1.19.16-r30, v1.21.10-r10, v1.23.8-r10, v1.25.3-r10, or later
Shared load balancers: v1.23.13-r0, v1.25.8-r0, v1.27.5-r0, v1.28.3-r0, or later
kubernetes.io/elb.client_timeout
String
Timeout for waiting for a request from a client. There are two cases:
  • If the client fails to send a request header to the load balancer during the timeout duration, the request will be interrupted.
  • If the interval between two consecutive request bodies reaching the load balancer is greater than the timeout duration, the connection will be disconnected.
The value ranges from 1 to 300 (in seconds). The default value is 60.
kubernetes.io/elb.member_timeout
String
Timeout for waiting for a response from a backend server. After a request is forwarded to the backend server, if the backend server does not respond within the duration specified by member_timeout, the load balancer will stop waiting and return HTTP 504 Gateway Timeout.
For details, see Configuring Timeout for a LoadBalancer Service.
Resource Tags
Table 11 Annotations
Type
kubernetes.io/elb.tags
String
Add resource tags to a load balancer. This parameter can be configured only when a load balancer is automatically created.
A tag is in the format of "key=value". Use commas (,) to separate multiple tags.
v1.23.11-r0, v1.25.6-r0, v1.27.3-r0, or later
HTTP/2
Table 12 Annotations of using HTTP/2
Type
kubernetes.io/elb.http2-enable
String
Whether HTTP/2 is enabled. Request forwarding using HTTP/2 improves the access performance between your application and the load balancer. However, the load balancer still uses HTTP/1.x to forward requests to the backend server.
Options:
  • true: enabled
  • false: disabled (default value)
Note: HTTP/2 can be enabled or disabled only when the listener uses HTTPS. This parameter is invalid and defaults to false when the listener protocol is HTTP.
For details, see Configuring HTTP/2 for a LoadBalancer Service.
Parameters for Automatically Creating a Load Balancer
Table 13 elb.autocreate data structure
Mandatory
Type
name
No
String
Name of the automatically created load balancer.
The value can contain 1 to 64 characters. Only letters, digits, underscores (_), hyphens (-), and periods (.) are allowed.
Default: cce-lb+service.UID
type
No
String
Network type of the load balancer.
  • public: public network load balancer
  • inner: private network load balancer
Default: inner
bandwidth_name
Yes for public network load balancers
String
Bandwidth name. The default value is cce-bandwidth-******.
No
String
Bandwidth mode.
  • bandwidth: billed by bandwidth
  • traffic: billed by traffic
Default: bandwidth
bandwidth_size
Integer
Bandwidth size. The value ranges from 1 Mbit/s to 2000 Mbit/s by default. Configure this parameter based on the bandwidth range allowed in your region.
The minimum increment for bandwidth adjustment varies depending on the bandwidth range.
  • The minimum increment is 1 Mbit/s if the allowed bandwidth does not exceed 300 Mbit/s.
  • The minimum increment is 50 Mbit/s if the allowed bandwidth ranges from 300 Mbit/s to 1000 Mbit/s.
  • The minimum increment is 500 Mbit/s if the allowed bandwidth exceeds 1000 Mbit/s.
bandwidth_sharetype
String
Bandwidth sharing mode.
  • PER: dedicated bandwidth
eip_type
String
EIP type.
  • 5_bgp: dynamic BGP
The specific type varies with regions. For details, see the EIP console.
vip_subnet_cidr_id
No
String
Subnet where a load balancer is located. The subnet must belong to the VPC where the cluster resides.
If this parameter is not specified, the ELB load balancer and the cluster are in the same subnet.
This field can be specified only for clusters of v1.21 or later.
vip_address
No
String
Private IP address of the load balancer. Only IPv4 addresses are supported.
The IP address must be in the ELB CIDR block. If this parameter is not specified, an IP address will be automatically assigned from the ELB CIDR block.
This parameter is available only in clusters of v1.23.11-r0, v1.25.6-r0, v1.27.3-r0, or later versions.
available_zone
Yes
Array of strings
AZ where the load balancer is located.
This parameter is available only for dedicated load balancers.
l4_flavor_name
Yes
String
Flavor name of the layer-4 load balancer.
l7_flavor_name
No
String
Flavor name of the layer-7 load balancer.
This parameter is available only for dedicated load balancers. The value of this parameter must be the same as that of l4_flavor_name, that is, both are elastic specifications or fixed specifications.
elb_virsubnet_ids
No
Array of strings
Subnet where the backend server of the load balancer is located. If this parameter is left blank, the default cluster subnet is used. Load balancers occupy different number of subnet IP addresses based on their specifications. Do not use the subnet CIDR blocks of other resources (such as clusters and nodes) as the load balancer CIDR block.
Example:
"elb_virsubnet_ids": [
   "14567f27-8ae4-42b8-ae47-9f847a4690dd"
Table 14 elb.health-check-option data structure
Mandatory
Type
delay
No
String
Health check interval (s)
Value range: 1 to 50. Default value: 5
timeout
No
String
Health check timeout, in seconds.
Value range: 1 to 50. Default value: 10
max_retries
No
String
Maximum number of health check retries.
Value range: 1 to 10. Default value: 3
protocol
No
String
Health check protocol.
Value options: TCP or HTTP
path
No
String
Health check URL. This parameter needs to be configured when the protocol is HTTP.
Default value: /
Value range: 1-80 characters
Table 15 elb.health-check-options
Mandatory
Type
target_service_port
Yes
String
Port for health check specified by spec.ports. The value consists of the protocol and port number, for example, TCP:80.
monitor_port
No
String
Re-specified port for health check. If this parameter is not specified, the service port is used by default.
Ensure that the port is in the listening state on the node where the pod is located. Otherwise, the health check result will be affected.
delay
No
String
timeout
No
String
max_retries
No
String
protocol
No
String
Default value: protocol of the associated Service
Value options: TCP, UDP, or HTTP
path
No
String
Default value: /
Table 16 elb.session-affinity-option data structure
Mandatory
Type
persistence_timeout
Yes
String
Sticky session timeout, in minutes. This parameter is valid only when elb.session-affinity-mode is set to SOURCE_IP.