Configuring the Threshold
You can configure monitoring indicator thresholds to monitor the health status of indicators on FusionInsight Manager. If abnormal data occurs and the preset conditions are met, the system triggers an alarm and displays the alarm information on the alarm page.
  2. Choose O&M > Alarm > Thresholds.
  3. Select a monitoring indicator for a specified host or service in the cluster.
    Figure 1 Configuring indicator thresholds
    For example, after selecting Host Memory Usage, the information about this indicator threshold is displayed.
    • If the alarm sending switch is displayed as , an alarm is triggered if the alarm threshold is reached.
    • The alarm ID and alarm name contain the alarm information that is triggered by the threshold:
    • FusionInsight Manager checks whether the value of each monitored indicator reaches the threshold. If the number of consecutive check times is equal to the value of Trigger Count, and the threshold is not reached in these checks, the system sends an alarm.
    • The value can be customized. Check Period (s) indicates the interval for the system to check monitoring indicators.
    • Rules for triggering an alarm.
  4. Click Create Rule to add rules used for monitoring indicators.
    Table 1 Monitoring indicator rule parameters
    Value
    Rule Name
    CPU_MAX (example value)
    Name of a rule.
    Alarm Severity
    • Critical
    • Major
    • Minor
    • Warning
    Alarm Severity
    • Critical
    • Major
    • Minor
    • Warning
    Threshold Type
    • Max value
    • Min value
    You can select the maximum or minimum value of an indicator. Setting this parameter to Max value, the system generates an alarm when the actual value of the indicator is greater than the threshold. Setting this parameter to Min value, the system generates an alarm when the actual value of the indicator is less than the threshold.
    Date
    • Daily
    • Weekly
    • Others
    This parameter is used to set the date when the rule takes effect.
    Add Date
    09-30
    This parameter is available only when Date is set to Others. You can set the date when the rule takes effect. Multiple options are available.
    Thresholds
    Start and End Time: 00: 00 to 08:30
    This parameter is used to set the time range when the rule takes effect.
    Threshold: 10
    Specifies the threshold of the rule monitoring indicator.
    For the last parameter in the table, you can click or to add or delete multiple start and end time or alarm indicator thresholds.
  5. Click OK to save the rules.
  6. Locate the row that contains an added rule, and click Apply in the Operation column. The value of Effective for this rule changes as Yes.
    You can apply a new rule only after clicking Cancel.
Monitoring Indicator Reference
FusionInsight Manager alarm monitoring indicators are categorized into node information indicators and cluster service indicators. Table 2 describes the indicators whose thresholds can be configured on nodes. For all the monitoring indicator list, see the M.
Table 2 Monitoring indicators on each node
Monitoring Indicator Group Name
Indicator Name
Default Threshold
CPU
Host CPU Usage
This indicator reflects the computing and control capabilities of the current cluster in a measurement period. By observing the indicator value, you can better understand the overall resource usage of the cluster.
90.0%
Disk
Disk Usage
Indicates the disk usage of a host.
90.0%
Disk Inode Usage
Indicates the disk inode usage in a measurement period.
80.0%
Memory
Host Memory Usage
Indicates the average memory usage at the current time.
90.0%
Host Status
Host File Handle Usage
Indicates the usage of file handles of the host in a measurement period.
80.0%
Host PID Usage
Indicates the PID usage of a host.
90%
Network Status
TCP Ephemeral Port Usage
Indicates the usage of temporary TCP ports of the host in a measurement period.
80.0%
Network Reading
Read Packet Error Rate
Indicates the read packet error rate of the network interface on the host in a measurement period.
0.5%
Read Packet Dropped Rate
Indicates the read packet dropped rate of the network interface on the host in a measurement period.
0.5%
Read Throughput Rate
Indicates the average read throughput (at MAC layer) of the network interface in a measurement period.
80%
Network Writing
Write Packet Error Rate
Indicates the write packet error rate of the network interface on the host in a measurement period.
0.5%
Write Packet Dropped Rate
Indicates the write packet dropped rate of the network interface on the host in a measurement period.
0.5%
Write Throughput Rate
Indicates the average write throughput (at MAC layer) of the network interface in a measurement period.
80%
Process
Uninterruptible Sleep Process
Indicates the number of D state processes on the host in a measurement period.
0
omm Process Usage
Indicates the usage of the omm process within a measurement period.
90
Table 3 Cluster service indicators
Service
Indicator Name
Default Threshold
DBService
Database
Database Connections Usage
Indicates the usage of the number of database connections.
90%
Disk Space Usage of the Data Directory
Disk space usage of the data directory.
80%
Flume
Agent
Heap Memory Usage Calculate
Indicates the Flume heap memory usage.
95.0%
Flume Direct Memory Usage Statistics
Indicates the Flume direct memory usage.
80.0%
Flume Non-heap Memory Usage
Indicates the Flume non-heap memory usage.
80.0%
Total GC duration of Flume process
Indicates the Flume total GC time.
12000ms
HBase
GC
GC time for old generation
Indicates the total GC time of RegionServer.
5000ms
Indicates the total GC time of HMaster.
5000ms
CPU and Memory
RegionServer Direct Memory Usage Statistics
Indicates the RegionServerReg direct memory usage.
90%
RegionServer Heap Memory Usage Statistics
Indicates the RegionServer heap memory usage.
90%
HMaster Direct Memory Usage
Indicates the HMaster direct memory usage.
90%
HMaster Heap Memory Usage Statistics
Indicates the HMaster heap memory usage.
90%
Service
Regions
Indicates the number of regions of a RegionServer.
2000
Region in transaction count over threshold
Number of regions that are in the RIT state and reach the threshold duration.
Replication
Replication sync failed times
Indicates the number of times that DR data fails to be synchronized.
Queue
Compaction Queue Size
Compaction queue size.
100
HDFS
File and Block
Lost Blocks
Number of missing copy blocks in the HDFS file system.
0
Blocks Under Replicated
Total number of blocks that need to be replicated by the NameNode.
1000
RPC
Average Time of Active NameNode RPC Processing
Indicates the average RPC processing time.
100ms
Average Time of Active NameNode RPC Queuing
Indicates the average RPC queuing time.
200ms
Disk
Disk Usage
Indicates the HDFS disk usage.
80%
Percentage of DataNode Capacity
Indicates the disk usage of DataNodes in the HDFS.
80%
Percentage of Reserved Space for Replicas of Unused Space
Indicates the percentage of the reserved disk space of all the copies to the total unused disk space of DataNodes.
90%
Resource
Faulty DataNodes
Indicates the number of faulty DataNodes.
3
NameNode Non Heap Memory Usage Statistics
Indicates the percentage of NameNode non-heap memory usage.
90%
NameNode Direct Memory Usage Statistics
Indicates the percentage of direct memory used by NameNodes.
90%
NameNode Heap Memory Usage Statistics
95%
DataNode Non Heap Memory Usage Statistics
Indicates the percentage of DataNode non-heap memory usage.
90%
DataNode Direct Memory Usage Statistics
Indicates the percentage of direct memory used by DataNodes.
90%
DataNode Heap Memory Usage Statistics
95%
Garbage Collection
GC Time
Indicates the Garbage collection (GC) duration of NameNodes per minute.
12000ms
GC Time
Indicates the GC duration of DataNodes per minute.
12000ms
Hive
HQL
Percentage of HQL Statements That Are Executed Successfully by Hive
Indicates the percentage of HQL statements that are executed successfully by Hive.
90.0%
Background
Background Thread Usage
Indicates the percentage of Background thread usage.
90%
GC
Total GC Time in Milliseconds
Indicates the total GC time of MetaStore.
12000ms
Indicates the total GC time of HiveServer.
12000ms
Capacity
Percentage of HDFS Space Used by Hive to the Available Space
Indicates the percentage of HDFS space used by Hive to the available space.
85.0%
CPU and Memory
MetaStore Direct Memory Usage Statistics
Indicates the MetaStore direct memory usage.
95%
MetaStore Non-Heap Memory Usage Statistics
Indicates the MetaStore non-heap memory usage.
95%
MetaStore Heap Memory Usage Statistics
Indicates the MetaStore heap memory usage.
95%
HiveServer Direct Memory Usage Statistics
Indicates the HiveServer direct memory usage.
95%
HiveServer Non-Heap Memory Usage Statistics
Indicates the HiveServer non-heap memory usage.
95%
HiveServer Heap Memory Usage Statistics
Indicates the HiveServer heap memory usage.
95%
Session
Percentage of Sessions Connected to the HiveServer to Maximum Number of Sessions Allowed by the HiveServer
Indicates the percentage of the number of sessions connected to the HiveServer to the maximum number of sessions allowed by the HiveServer.
90.0%
Kafka
Partition
Percentage of Partitions That Are Not Completely Synchronized
Indicates the percentage of partitions that are not completely synchronized to total partitions.
50%
Other
Unavailable Partition Percentage
Disk usage of the disk where the Broker data directory is located.
40%
User Connection Usage on Broker
User connection usage on the broker.
80%
Disk
Broker Disk Usage
Indicates the disk usage of the disk where the Broker data directory is located.
80%
Process
Broker GC Duration per Minute
Indicates the GC duration of the Broker process per minute.
12000ms
Heap Memory Usage of Kafka
Indicates the Kafka heap memory usage.
95%
Kafka Direct Memory Usage
Indicates the Kafka direct memory usage.
95%
Loader
Memory
Indicates the Loader heap memory usage.
95%
Loader Direct Memory Usage Statistics
Indicates the Loader direct memory usage.
80.0%
Non heap Memory Usage Calculate
Indicates the Loader non-heap memory usage.
80%
GC
Total GC time in milliseconds
Indicates the total GC time of Loader.
12000ms
MapReduce
Garbage Collection
GC Time
Indicates the GC time.
12000ms
Resource
JobHistoryServer Direct Memory Usage Statistics
Indicates the JobHistoryServer direct memory usage.
90%
JobHistoryServer Non Heap Memory Usage Statistics
Indicates the JobHistoryServer non-heap memory usage.
90%
JobHistoryServer Heap Memory Usage Statistics
95%
Oozie
Memory
Indicates the Oozie heap memory usage.
95.0%
Oozie Direct Buffer Resource Percentage
Indicates the Oozie direct memory usage.
80.0%
Non Heap Memory Usage Calculate
Indicates the Oozie non-heap memory usage.
80%
GC
Total GC duration of Oozie process
Indicates the Oozie total GC time.
12000ms
Spark2x
Memory
JDBCServer2x Heap Memory Usage Statistics
Indicates the JDBCServer2x heap memory usage.
95%
JDBCServer2x Direct Memory Usage Statistics
Indicates the JDBCServer2x direct memory usage.
95%
JDBCServer2x Non-Heap Memory Usage Statistics
Indicates the JDBCServer2x non-heap memory usage.
95%
JobHistory2x Direct Memory Usage Statistics
Indicates the JobHistory2x direct memory usage.
95%
JobHistory2x Non-Heap Memory Usage Statistics
Indicates the JobHistory2x non-heap memory usage.
95%
JobHistory2x Heap Memory Usage Statistics
Indicates the JobHistory2x heap memory usage.
95%
IndexServer2x Direct Memory Usage Statistics
Indicates the IndexServer2x direct memory usage.
95%
IndexServer2x Heap Memory Usage Statistics
ndicates the IndexServer2x heap memory usage.
95%
IndexServer2x Non-Heap Memory Usage Statistics
Indicates the IndexServer2x non-heap memory usage.
95%
GC number
Full GC Number of JDBCServer2x
Indicates the total GC number of JDBCServer2x.
12
Full GC Number of JobHistory2x
Indicates the total GC number of JobHistory2x.
12
Full GC Number of IndexServer2x
Indicates the total GC number of IndexServer2x.
12
GC Time
Indicates the total GC time of JDBCServer2x.
12000ms
Indicates the total GC time of JobHistory2x.
12000ms
Indicates the total GC time of IndexServer2x.
12000ms
Storm
Cluster
Number of Available Supervisors
Indicates the number of available Supervisor processes in the cluster in a measurement period.
Slot Usage
Indicates the slot usage in the cluster in a measurement period.
80.0%
Nimbus
Indicates the Nimbus heap memory usage.
80%
Yarn
Resource
NodeManager Direct Memory Usage Statistics
Indicates the percentage of direct memory used by NodeManagers.
90%
NodeManager Heap Memory Usage Statistics
Indicates the percentage of NodeManager heap memory usage.
95%
NodeManager Non Heap Memory Usage Statistics
Indicates the percentage of NodeManager non-heap memory usage.
90%
ResourceManager Direct Memory Usage Statistics
90%
ResourceManager Heap Memory Usage Statistics
Indicates the ResourceManager heap memory usage.
95%
ResourceManager Non Heap Memory Usage Statistics
Indicates the ResourceManager non-heap memory usage.
90%
CPU and Memory
Pending Memory
Pending memory capacity.
83886080MB
Other
Failed Applications of root queue
Number of failed tasks in the root queue.
50
Terminated Applications of root queue
Number of killed tasks in the root queue.
50
Garbage collection
GC Time
Indicates the GC duration of NodeManager per minute.
12000ms
GC Time
Indicates the GC duration of ResourceManager per minute.
12000ms
Application
Pending Applications
Pending tasks.
60
ZooKeeper
Connection
ZooKeeper Connections Usage
Indicates the percentage of the used connections to the total connections of ZooKeeper.
80%
CPU and Memory
Indicates the ZooKeeper direct memory usage.
95%
Direct Memory Usage Calculate
Indicates the ZooKeeper heap memory usage.
80%
GC
ZooKeeper GC Duration per Minute
Indicates the GC time of ZooKeeper every minute.
12000ms
meta
OBS Meta data Operations
Average Time for Calling the OBS Metadata API
Average time for calling the OBS metadata APIs.
500ms
Success Rate for Calling the OBS Metadata API
Success rate of calling the OBS metadata APIs
99.0%
OBS data write operation
Success Rate for Calling the OBS Write API
Success rate of calling the OBS data write APIs.
99.0%
OBS data read operation
Success Rate for Calling the OBS Data Read API
Success rate of calling the OBS data read operation APIs.
99.0%
Ranger
GC
UserSync GC Duration
UserSync garbage collection (GC) duration.
12000ms
RangerAdmin GC Duration
RangerAdmin garbage collection (GC) duration.
12000ms
TagSync GC Duration
TagSync garbage collection (GC) duration.
12000ms
CPU and Memory
UserSync Non-Heap Memory Usage
UserSync non-heap memory usage in percentage.
80.0%
UserSync Direct Memory Usage
UserSync direct memory usage in percentage.
80.0%
UserSync Heap Memory Usage
UserSync heap memory usage in percentage.
95.0%
RangerAdmin Non-Heap Memory Usage
RangerAdmin non-heap memory usage.
80.0%
RangerAdmin Heap Memory Usage
RangerAdmin heap memory usage in percentage.
95.0%
RangerAdmin Direct Memory Usage
RangerAdmin direct memory usage.
80.0%
TagSync Direct Memory Usage
TagSync direct memory usage in percentage.
80.0%
TagSync Non-Heap Memory Usage
TagSync non-heap memory usage in percentage.
80.0%
TagSync Heap Memory Usage
TagSync heap memory usage in percentage.
95.0%
ClickHouse
Cluster Quota
Clickhouse service quantity quota usage in ZooKeeper
Quota of the ZooKeeper nodes used by the ClickHouse service.
90%
Capacity quota usage of the Clickhouse service in ZooKeeper
Capacity quota of ZooKeeper directory used by the ClickHouse service.
90%
IoTDB
GC
IoTDBServer GC Duration
IoTDBServer garbage collection (GC) duration.
12000ms
CPU and Memory
IoTDBServer Heap Memory Usage
IoTDBServer heap memory usage in percentage.
90%
IoTDBServer Direct Memory Usage
IoTDBServer direct memory usage in percentage.
90%
