Updated on 2026-09-02 GMT+08:00
Monitored BMS Events
Event monitoring provides event data reporting, query, and alarm reporting. You can create alarm rules for both system events and custom events. When specific events occur, Cloud Eye generates alarms for you.
Namespace
SYS.BMS
Monitored Events
Table 1 Supported BMS events
Event Name
Event ID
Event Severity
Handling Solution
Impact
Uncorrectable ECC error on GPU SRAM
SRAMUncorrectableEccError
Major
Uncorrectable ECC errors occur on GPU SRAM.
If services are affected, submit a service ticket.
The GPU hardware may be faulty. As a result, the SRAM is faulty, and services exit abnormally.
BMS restarted
osReboot
Major
The BMS was restarted
  • On the management console
  • By calling APIs
  • Deploy service applications in HA mode.
  • After the BMS is restarted, check whether services recover.
Services are interrupted.
Unexpected restart
serverReboot
Major
The BMS was restarted unexpectedly due to:
  • OS faults
  • Hardware faults
BMS stopped
osShutdown
Major
The BMS was stopped
  • By calling APIs
BMS unexpected shutdown
serverShutdown
Major
The BMS was stopped unexpectedly due to:
  • Unexpected power-off
  • Hardware faults
Network disconnection
linkDown
Major
The BMS network was disconnected due to:
  • Unexpected BMS stop or restart
  • Switch faults
  • Gateway faults
PCIe error
pcieError
Major
The PCIe device on the BMS was faulty, including:
  • Main board faults
  • PCIe device faults
The network or disk read/write services are affected.
Disk fault
diskError
Major
The disks of the BMS were faulty, including:
  • Disk backplane faults
  • Disk faults
Data read/write services are affected, or the BMS cannot be started.
Storage error
storageError
Major
The BMS failed to connect to EVS disks due to:
  • SDI card faults
  • Remote storage device faults
GPU infoROM error
gpuInfoROMAlarm
Major
The infoROM of the GPU is abnormal. ROM is an important storage area of the GPU firmware and stores key data loaded during startup.
Non-critical services can continue to use the GPU. For critical services, submit a service ticket to resolve this issue.
  1. Restart the VM and check that the issue is not caused by a temporary cache or communication error.
  2. If the fault persists after the restart, the hardware may be faulty. Submit a service ticket to check whether the GPU needs to be replaced.
Services will not be affected. If ECC errors are reported on a GPU, faulty pages may not be automatically retired and services are affected.
Double-bit ECC error on GPU
doubleBitEccError
Major
A double-bit error occurs in the ECC memory of the GPU. The ECC cannot correct the error, which may cause program breakdown.
  1. If services are interrupted, restart the services.
  2. If services cannot be restarted, restart the VM where services are running.
  3. If services still cannot be restored, submit a service ticket.
Services may be interrupted. After faulty pages are retired, the GPU can continue to be used.
Too many retired pages on GPU
gpuTooManyRetiredPagesAlarm
Major
The GPU has too many ECC-retired pages. When an uncorrectable ECC error occurs on a GPU memory page, the GPU marks the page as retired.
If there are too many ECC errors, services may be affected.
  1. If there are too many retired pages and the GPU memory capacity decreases too much, the system performance may deteriorate.
  2. If there are too many retired pages and the GPU memory capacity decreases too much, the system may run unstably.
ECC error on GPU A100
gpuA100EccAlarm
Major
An ECC error occurred on the GPU.
ECC alarm generated on GPU Ant1
gpuAnt1EccAlarm
Major
GPU ECC memory page retirement failure
eccPageRetirementRecordingFailure
Major
Automatic page retirement failed due to ECC errors.
Services may be interrupted, and memory page retirement fails. As a result, services cannot no longer use the GPU.
GPU ECC page retirement
eccPageRetirementRecordingEvent
Minor
Memory pages are automatically retired due to ECC errors.
Generally, this alarm is generated together with the ECC error alarm. If this alarm is generated independently, services are not affected.
Too many single-bit ECC errors on GPU
highSingleBitEccErrorRate
Major
There are too many single-bit errors occurring in the ECC memory of the GPU.
Single-bit errors can be automatically rectified. These errors generally do not affect GPU-related applications.
GPU card not found
gpuDriverLinkFailureAlarm
Major
A GPU link is normal, but it cannot be found by the NVIDIA driver.
1. Try to restart the VM to restore your services.
2. If services still cannot be restored, submit a service ticket.
The GPU cannot be found.
GPU link faulty
gpuPcieLinkFailureAlarm
Major
GPU hardware information cannot be queried through lspci due to a GPU link fault.
The driver cannot use the GPU.
VM GPU lost
vmLostGpuAlarm
Major
The number of GPUs on the VM is less than the number specified in the specifications.
GPUs get lost.
GPU memory page faulty
gpuMemoryPageFault
Major
The GPU memory page is faulty, which may be caused by applications, drivers, or hardware.
The GPU hardware may be faulty. As a result, the GPU memory is faulty, and services exit abnormally.
GPU image engine faulty
graphicsEngineException
Major
The GPU image engine is faulty, which may be caused by applications, drivers, or hardware.
The GPU hardware may be faulty. As a result, the image engine is faulty, and services exit abnormally.
GPU temperature too high
highTemperatureEvent
Major
The GPU temperature is too high.
If the GPU temperature exceeds the threshold, the GPU performance may deteriorate.
GPU NVLink faulty
nvlinkError
Major
A hardware fault occurs on the NVLink.
The NVLink link is faulty and unavailable.
System maintenance inquiring
system_maintenance_inquiring
Major
The scheduled BMS maintenance task is being inquired.
Authorize the maintenance.
None
System maintenance waiting
system_maintenance_scheduled
Major
The scheduled BMS maintenance task is waiting to be executed.
Clarify the impact on services during the execution window.
None
System maintenance canceled
system_maintenance_canceled
Major
The scheduled BMS maintenance is canceled.
None
None
System maintenance executing
system_maintenance_executing
Major
BMSs are being maintained as scheduled.
After the maintenance is complete, check whether services are affected.
System maintenance completed
system_maintenance_completed
Major
The scheduled BMS maintenance is completed.
Wait until the BMSs become available and check whether services recover.
None
System maintenance failure
system_maintenance_failed
Major
The scheduled BMS maintenance task failed.
Contact O&M personnel.
GPU Xid error
commonXidError
Major
A Xid event occurs, indicating a GPU problem.
A Xid error is caused by GPU hardware, driver, or application problems, which may result in abnormal service exit.
NPU: device not found by npu-smi info
NPUSMICardNotFound
Major
The Ascend driver is faulty, or the NPU is disconnected.
Transfer this issue to the Ascend or hardware team for handling.
The NPU cannot be used normally.
NPU: PCIe link error
PCIeErrorFound
Major
The lspci command returns rev ff, indicating that the NPU is abnormal.
Restart the BMS. If the issue persists, transfer it to the hardware team for processing.
NPU: device not found by lspci
LspciCardNotFound
Major
The NPU is disconnected.
Transfer this issue to the hardware team for handling.
NPU: overtemperature
TemperatureOverUpperLimit
Major
The temperature of DDR or software is too high.
Stop services, restart the BMS, check the heat dissipation system, and reset the devices.
The BMS may be powered off, and devices may not be found.
NPU: uncorrectable ECC error
UncorrectableEccErrorCount
Major
There are uncorrectable ECC errors on the NPU.
If services are affected, replace the NPU with another one.
NPU: request for BMS restart
RebootVirtualMachine
Warning
The BMS needs to be restarted.
Collect the required information and restart the BMS.
NPU: request for SoC reset
ResetSOC
Warning
The SoC needs to be reset.
Collect the required information and reset the SoC.
NPU: request for restart AI process
RestartAIProcess
Warning
The AI process needs to be restarted.
Collect the required information and restart the AI process.
The current AI task will be interrupted.
NPU: error codes
NPUErrorCodeWarning
Major
There are a large number of NPU error codes indicating major or higher-level errors. You can further locate the faults based on the error codes.
Locate the faults according to the Black Box Error Code Information List and Health Management Error Definition.
nvidia-smi suspended
nvidiaSmiHangEvent
Major
nvidia-smi timed out.
The driver may report an error during service running.
nv_peer_mem loading error
NvPeerMemException
Minor
The NVLink or nv_peer_mem cannot be loaded.
Restore or reinstall the NVLink.
nv_peer_mem cannot be used.
Fabric Manager error
NvFabricManagerException
Minor
The BMS meets the NVLink conditions and NVLink is installed, but Fabric Manager is abnormal.
NVLink cannot be used.
IB card error
InfinibandStatusException
Major
The IB card or its physical status is abnormal.
The IB card cannot work normally.
GPU throttle alarm
gpuClocksThrottleReasonsAlarm
Warning
  1. The GPU power may exceed the maximum operating power threshold (continuous full load). The clock frequency automatically decreases to prevent the GPU from being damaged.
  2. The GPU temperature may exceed the maximum operating temperature threshold (continuous full load). The clock frequency automatically decreases to reduce heat.
  3. The GPU may remain idle, with the clock frequency automatically decreasing to reduce power consumption.
  4. Hardware faults may cause a decrease in clock frequency.
Check whether the clock frequency decrease is caused by hardware faults. If yes, transfer it to the hardware team.
The GPU slows down, resulting in less powerful compute.
Pending page retirement for GPU DRAM ECC
gpuRetiredPagesPendingAlarm
Major
  1. An ECC error occurred on the hardware. DRAM pages need to be retired.
  2. An uncorrectable ECC error occurred on the GPU memory page, and the page needs to be retired. However, the page is suspended and has not been retired yet.
  1. View the event details and check whether the value of retired_pages.pending is yes.
  2. Restart the GPU for automatic retirement.
The GPU cannot work properly.
Pending row remapping for GPU DRAM ECC
gpuRemappedRowsAlarm
Major
Some rows in the GPU memory have errors and need to be remapped. The faulty rows must be mapped to standby resources.
  1. View the event metric "RemappedRow" to check if there are any rows that have been remapped.
Insufficient resources for GPU DRAM ECC row remapping
gpuRowRemapperResourceAlarm
Major
  1. This event occurs on GPUs (Ampere and later architectures).
  2. The standby GPU memory row resources are exhausted, so row remapping cannot be continued.
Transfer the issue to the hardware team.
Correctable GPU DRAM ECC error
gpuDRAMCorrectableEccError
Major
  2. A correctable ECC error occurs in the DRAM of the GPU. However, the ECC mechanism can automatically rectify the error and programs are not affected.
  1. View the event metric "ecc.errors.corrected.volatile" to check whether there are any correctable ECC error values.
The GPU may not work properly.
Uncorrectable GPU DRAM ECC error
gpuDRAMUncorrectableEccError
Major
  2. An uncorrectable ECC error occurs in the DRAM of the GPU. This error cannot be automatically corrected using the ECC mechanism. The verification process affects system stability and may cause program crashes.
  1. View the event metric "ecc.errors.uncorrected.volatile" to check whether there are any uncorrectable ECC error values.
Inconsistent GPU kernel versions
gpuKernelVersionInconsistencyAlarm
Major
Inconsistent GPU kernel versions.
During driver installation, the GPU driver is compiled based on the kernel at that time. If the kernel versions are identified inconsistent, the kernel has been customized after the driver installation. In this case, the driver would become unavailable and needs to be reinstalled.
  1. Run the following commands to rectify the issue:
    rmmod nvidia_drm
    rmmod nvidia_modeset
    rmmod nvidia
    Then, run nvidia-smi. If the command output is normal, the issue has been rectified.
  1. If the preceding solution does not work, rectify the fault by referring to Why Is the GPU Driver Unavailable?
GPU monitoring dependency not met
gpuCheckEnvFailedAlarm
Major
The plug-in cannot identify the GPU driver library path.
  1. Check whether the driver is installed.
  2. Check whether the driver installation directory has been customized. The driver needs to be installed in the default installation directory /usr/bin/.
The GPU metrics cannot be collected.
Initialization failure of the GPU monitoring driver library
gpuDriverInitFailedAlarm
Major
The GPU driver is unavailable.
Run nvidia-smi to check whether the driver is unavailable. If the driver is unavailable, reinstall the driver by referring to Manually Installing a Tesla Driver on a GPU-accelerated ECS.
Initialization timeout of the GPU monitoring driver library
gpuDriverInitTAlarm
Major
The GPU driver initialization timed out (exceeding 10s).
  1. If the driver is not installed, install it by referring to Manually Installing a Tesla Driver on a GPU-accelerated ECS.
  2. If the driver is installed, run nvidia-smi to check whether the driver is available. If the driver is unavailable, reinstall the driver by referring to Manually Installing a Tesla Driver on a GPU-accelerated ECS.
  3. If the driver is properly installed, check whether the high-performance mode is enabled. If not, run nvidia-smi -pm 1 to enable it. P0 indicates the high-performance mode.
GPU metric collection timeout
gpuCollectMetricTimeoutAlarm
Major
The GPU metric collection timed out (exceeding 10s).
  1. If the library API timed out, run nvidia-smi to check whether the driver is available. If the driver is unavailable, reinstall the driver by referring to Manually Installing a Tesla Driver on a GPU-accelerated ECS.
  2. If the command execution timed out, check the system logs and determine whether there is an issue with the system.
GPU monitoring metric data is missing. As a result, subsequent metrics may fail to be collected.
GPU handle lost
gpuDeviceHandleLost
Major
The GPU metric information cannot be obtained, and the GPU may be lost.
  1. Run nvidia-smi to check whether there are any errors reported.
  2. Run nvidia-smi -L to check whether the number of GPUs is the same as the server specifications.
  3. Submit a service ticket to contact on-call support.
All metrics of the GPU are lost.
Failed to listen to the XID of the GPU
gpuDeviceXidLost
Major
Failed to listen to the XID metric.
  1. Check whether the GPU is lost or damaged.
  2. Submit a service ticket to contact on-call support.
Failed to obtain XID-related metrics of the GPU.
Multiple NPU HBM ECC errors
NpuHbmMultiEccInfo
Warning
There are NPU HBM ECC errors.
This event is only a reference for other events. You do not need to handle it separately.
The NPU may not work properly.
ReadOnly issues in OS
ReadOnlyFileSystem
Critical
The file system %s is read-only.
Check the disk health status.
The files cannot be written.
NPU: driver and firmware not matching
NpuDriverFirmwareMismatch
Major
The NPU's driver and firmware do not match.
Obtain the matched version from the Ascend official website and reinstall it.
NPUs cannot be used.
NPU: Docker container environment check
NpuContainerEnvSystem
Major
Docker was unavailable.
Check if Docker is normal.
Docker cannot be used.
Major
The container plug-in Ascend-Docker-Runtime was not installed.
Install the container plug-in Ascend-Docker-Runtime, or the container cannot use Ascend cards.
NPUs cannot be attached to Docker containers.
Major
IP forwarding was not enabled in the OS.
Check the net.ipv4.ip_forward configuration in the /etc/sysctl.conf file.
Docker containers have network communication problems.
Major
The shared memory of the container was too small.
The default shared memory is 64 MB, which can be modified as needed.
Method 1
Modify the default-shm-size field in the /etc/docker/daemon.json configuration file.
Method 2
Use the --shm-size parameter in the docker run command to set the shared memory size of a container.
Distributed training will fail due to insufficient shared memory.
NPU: RoCE NIC down
RoCELinkStatusDown
Major
The RoCE link of NPU card %d was down.
Check the NPU RoCE network port status.
The NPU NIC is unavailable.
NPU: RoCE NIC health status abnormal
RoCEHealthStatusError
Major
The RoCE network health status of NPU %d was abnormal.
Check the health status of the NPU RoCE NIC.
NPU: RoCE NIC configuration file /etc/hccn.conf not found
HccnConfNotExisted
Major
The RoCE NIC configuration file /etc/hccn.conf was not found.
Check whether the NIC configuration file /etc/hccn.conf can be found.
The RoCE NIC is unavailable.
GPU: basic components abnormal
GpuEnvironmentSystem
Major
The nvidia-smi command was abnormal.
Check whether the GPU driver is normal.
Major
The nvidia-fabricmanager version was inconsistent with the GPU driver version.
Check the GPU driver version and nvidia-fabricmanager version.
The nvidia-fabricmanager cannot work properly, affecting GPU usage.
Major
The container add-on nvidia-container-toolkit was not installed.
Install the container add-on nvidia-container-toolkit.
GPUs cannot be attached to Docker containers.
Local disk attachment inspection
MountDiskSystem
Major
The /etc/fstab file contains invalid UUIDs.
Ensure that the UUIDs in the /etc/fstab configuration file are correct, or the server may fail to be restarted.
The disk attachment process fails, preventing the server from restarting.
GPU: incorrectly configured dynamic route for Ant series server
GpuRouteConfigError
Major
The dynamic route of the NIC %s of an Ant series server was not configured or was incorrectly configured. CMD [ip route]: %s | CMD [ip route show table all]: %s.
Configure the RoCE NIC route correctly.
The NPU network communication will be interrupted.
NPU: RoCE port not split
RoCEUdpConfigError
Major
The RoCE UDP port was not split.
Check the RoCE UDP port configuration on the NPU.
The communication performance of NPUs is affected.
Warning of automatic system kernel upgrade
KernelUpgradeWarning
Major
Warning of automatic system kernel upgrade. Old version: %s; new version: %s.
System kernel upgrade may cause AI software exceptions. Check the system update logs and prevent the server from restarting.
The AI software may be unavailable.
NPU environment command detection
NpuToolsWarning
Major
The hccn_tool was unavailable.
Check whether the NPU driver is normal.
The IP address and gateway of the RoCE NIC cannot be configured.
Major
The npu-smi was unavailable.
Major
The ascend-dmi was unavailable.
Check whether ToolBox is properly installed.
ascend-dmi cannot be used for performance analysis.
Warning of an NPU driver exception
NpuDriverAbnormalWarning
Major
The NPU driver was abnormal.
Reinstall the NPU driver.
GPU: invalid RoCE NIC configuration
GpuRoceNicConfigIncorrect
Major
The RoCE NIC of the GPU is incorrectly configured.
The parameter plane network is abnormal, preventing the execution of the multi-node task.
Local disk replacement to be authorized
localdisk_recovery_inquiring
Major
The local disk is faulty. Local disk replacement authorization is in progress.
Authorize local disk replacement.
Local disks are unavailable.
Local disks being replaced
localdisk_recovery_executing
Major
Local disks are faulty and being replaced.
When the replacement is complete, check whether the local disks are available.
Local disks replaced
localdisk_recovery_completed
Major
Local disks are faulty and have been replaced.
Wait until the services are running properly and check whether local disks are available.
None
Local disk replacement failed
localdisk_recovery_failed
Major
Local disks are faulty and fail to be replaced.
NIC link disconnected
nicLinkDown
Major
A BMS NIC port is abnormal, including:
  • The optical module or network cable of the BMS network port or switch port is faulty.
  • The switch is faulty.
If a single port is faulty and the NIC is in bonding mode, traffic will fail over automatically.
The NIC bond redundancy fails or the services are interrupted.