How Can I Locate a Fault That Occurs with a Node?
Fault Locating
CCE allows you to locate a node fault using the CCE Node Problem Detector add-on (Locating a Node Fault Using the CCE Node Problem Detector Add-on). You can also refer to Locating a Node Fault by Performing a Self-Check to locate the fault.
If the fault persists, submit a service ticket.
CCE provides an add-on called CCE Node Problem Detector for you to locate faults occurred with nodes. In 1.16.0 and later versions of this add-on, a large number of check items have been added. They allow you to detect the exceptions of resources and components on nodes and locate the faults.
It is strongly recommended that you install this add-on or upgrade it to version 1.16.0 or later.
With this add-on, if an exception occurs with a node, you can view the abnormal metrics on the console.
You can also view the events reported by the add-on in node events and locate the faults based on the events.
Event |
Description |
OOMKilling |
Check whether OOM events occurred and are reported. Handling suggestions: Check Item 1: Whether the Node Is Overloaded |
TaskHung |
Check whether taskHung events occurred and are reported. |
KernelOops |
Check the kernel null pointer panic errors. |
ConntrackFull |
Check whether the conntrack table is full. |
FrequentKubeletRestart |
Check whether kubelet restarts frequently. |
FrequentDockerRestart |
Check whether Docker restarts frequently. |
FrequentContainerdRestart |
Check whether containerd restarts frequently. |
CRIProblem |
Check the CRI components. |
KUBELETProblem |
Check the kubelet. |
NTPProblem |
Check the NTP service. |
PIDProblem |
Check whether PIDs are sufficient. |
FDProblem |
Check whether file handles are sufficient. |
MemoryProblem |
Check whether the overall node memory is sufficient. |
CNIProblem |
Check the CNI components. |
KUBEPROXYProblem |
Check the kube-proxy. |
ReadonlyFilesystem |
Check whether the Remount root filesystem read-only error occurred in the system kernel. Possible cause: The data disks were detached from the ECS by mistake, or the VDB disk of the node has been deleted. Handling suggestions: |
DiskReadonly |
Check whether the system disk, Docker disk, and kubelet disk are read-only. Possible cause: The data disks were detached from the ECS by mistake, or the VDB disk of the node has been deleted. Handling suggestions: |
DiskProblem |
Check the disk usage and whether the key logical disk is properly attached to the node. Check the usage of the system disk, Docker disk, and kubelet disk, and check whether the Docker and kubelet disks are properly attached to the ECS. |
PIDPressure |
Check whether PIDs are sufficient. Handling suggestions: If there are not enough PIDs available, adjust the upper limit of PIDs as needed. |
MemoryPressure |
Check whether the allocable memory for the containers is sufficient. |
DiskPressure |
Check the usage of kubelet and Docker disks and inodes. Handling suggestions: Expand the capacity of the data disks. |
- Log in to the CCE console.
- Click the cluster name to access the cluster console. Choose Nodes in the navigation pane. In the right pane, click the Nodes tab.
- Locate the row containing the target node, choose More > View YAML in the Operation column, and check the Status field of the node.
The node is in the NotReady state.
- Check the node status and verify whether the value of PIDPressure, DiskPressure, or MemoryPressure becomes True. If any of them becomes True, you can find the appropriate solution based on the exception keyword.
- Check the key components on the node and the logs of these components. The key components on a node include a kubelet and the node runtime (Docker or containerd). For details, see Checking Key Components of the Node.
- Check the kubelet.
Check whether the kubelet and its logs are normal. If there is an exception, see Abnormal kubelet.
- Check the runtime (Docker or containerd).
- Check the runtime of the node. If you are not sure whether the runtime is Docker or containerd, log in to the CCE console and view the runtime of the node.
- If there is an exception, see Abnormal Runtime.
- Check the NTP.
- Check whether the NTP, its logs, and the configurations are normal.
- If there is an exception, see Abnormal NTP.
- Check the node monitoring data and see whether the CPU, memory, and network resources of the node are normal. If there is an exception, rectify the fault by referring to Memory Pressure.
The node is in the Unknown state.
- Log in to the ECS console and check whether the node is present in the ECS list.
- Check whether the node is running properly.
- Check whether the kubelet and its logs are normal. If there is an exception, see Abnormal kubelet.
- Check the network connectivity of the node.
Common Problems and Troubleshooting Methods
- Checking a Node
- Checking the Node Monitoring Data
- Checking the Node Events
- Verifying Whether the ECS Has Been Deleted or Is Faulty
- Verifying Whether the ECS Can Be Logged In
- Checking the Node Security Group
- Checking the Disks Attached to the Node
- Checking Key Components of the Node
- Verifying Whether the Node DNS Address Is Properly Configured
Checking a Node
- Click the name of the target cluster to access the cluster console.
- In the navigation pane, choose Nodes. In the right pane, click the Nodes tab, locate the row containing the unavailable node, and view its status. (If NPD 1.6.10 or a later version is installed in the cluster, you will see a message indicating that the metrics for the unavailable node are abnormal. In this case, you can move the cursor to the upper part to view the specific problem. If the add-on is not installed, you can rectify the fault by referring to the check items.)
- In the navigation pane, choose Nodes. In the right pane, click the Nodes tab, locate the row containing the abnormal node, and click Monitor in the Operation column.
On the top of the displayed page, click More Monitoring Data to go to the AOM console and view historical monitoring records. If the CPU or memory usage of the node is too high, it can lead to high network latency or trigger system OOM, causing the node to be marked as unavailable.
- In the navigation pane, choose Nodes. In the right pane, click the Nodes tab, locate the row containing the abnormal node, click View Events in the Operation column, and check whether any abnormal event is reported. (The NPD add-on must be installed.)
- Log in to the CCE console, click the name of the target cluster to access the cluster console, and view the name of the unavailable node.
- Log in to the ECS console, search for the node, and check the ECS status.
- If the ECS has been deleted, go back to the CCE console, delete the node from the node list, and create another one.
- If the ECS is stopped or frozen, restore it first. It takes about 3 minutes to restore the node.
- If the ECS is faulty, restart it to rectify the fault.
- If the ECS is available, rectify the fault by referring to Checking Key Components of the Node.
- Log in to the ECS console.
- Check whether the node name displayed on the ECS console is the same as that on the VM and whether the password or key can be used to log in to the node.
If the node names are inconsistent and the password or key cannot be used to log in to the node, Cloud-Init problems occurred when the ECS was created. In this case, you can restart the node and then submit a service ticket to the ECS personnel to locate the root cause.
- The node security group was changed.
- Log in to the VPC console. In the navigation pane, choose Access Control > Security Groups and find the master node security group of the cluster.
- Search for the name of the security group that contains the cluster name and -cce-control-. The name of a master node security group is in the format of cluster-name-cce-control-random-ID.
- Check whether the security group rules have been changed. For details about security groups, see How Can I Configure a Security Group Rule for a Cluster?
- The node security group rules must contain a policy that allows the communication between the master nodes and the worker nodes.
- Check whether such a security group policy is present.
- When adding a node to the cluster, add the security group rules listed in Table 2 to the cluster-name-cce-control-random-ID security group to ensure the availability of the added node. This is necessary if a secondary CIDR block is added to the VPC of the node subnet and the subnet is in the secondary CIDR block. However, if a secondary CIDR block has already been added to the VPC during cluster creation, this step is not required.
- For details about security groups, see How Can I Configure a Security Group Rule for a Cluster?
- By default, a 100-GiB data disk is attached to a node for runtime purposes. You have the option to attach additional data disks to the node if needed. If the data disk is detached or damaged, the runtime becomes abnormal and the node becomes unavailable.
- You need to check whether the data disks of the node are detached from it. If they are, you are advised to create a node and delete the unavailable node. (To minimize risks, you are not advised to perform operations on the CCE nodes through the ECS console.)
kubelet
Log in to the target node, run the following command on it, and check the kubelet:
systemctl status kubelet
The following shows an example of the expected output.
- View the kubelet logs.
journalctl -u kubelet
Runtime
- Docker
- containerd
- NTP
- Log in to the target node and check whether any domain name resolution failure is recorded in /var/log/cloud-init-output.log:
cat /var/log/cloud-init-output.log | grep resolv
If information similar to the following is displayed, the domain name cannot be resolved:
Could not resolve host: xxx ; Unknown error
- Ping the domain name that cannot be resolved on the node:
ping xxx
If the domain name cannot be pinged, the DNS cannot resolve the IP address. You need to verify if the DNS address in the /etc/resolv.conf file matches the configuration on the VPC subnet. In most cases, the DNS address in the file is improperly configured, leading to the inability to resolve domain names.
Common Issues and Solutions
PID Pressure
Possible cause
The pods on the node are using up a large number of PIDs, causing a shortage of available PIDs on the node. By default, CCE reserves 10% of the available PIDs for pods.
Symptom
If the number of available PIDs on a node is lower than the specified value of pid.available, the PIDPressure of the node will be set to True, resulting in the eviction of pods running on that node. For details about node eviction, see Node-pressure Eviction.
Solution
- Check the maximum number of PIDs on the node and the processes that use the most PIDs:
sysctl kernel.pid_max # Check the maximum number of PIDs. ps -eLf|awk '{print $2}' | sort -rn| head -n 1 #: Check the processes that use the most PIDs on the node.
- Check the top five processes that use the most PIDs:
ps -elT | awk '{print $4}' | sort | uniq -c | sort -k1 -g | tail -5
The following shows an example of the expected output:
17 1211619 18 3739112 18 5299 24 964 25 3739756
The first column shows the number of PIDs used by each process, while the second column displays the current process IDs. You can locate the process and associated pods with the given process ID, analyze the reason for excessive PID usage, and optimize the relevant code accordingly.
- Reduce the load of the node.
- To restart the node, go to the ECS console and restart it. (Be cautious when restarting the node because it may cause interruptions to your services.)
Memory Pressure
Possible cause
The pods on the node are using up a large amount of memory, causing a shortage of available memory on the node. By default, the available memory of a CCE node is 100 MiB.
Symptom
- If the number of available memory resources on a node is lower than the specified value of memory.available, the MemoryPressure of the node will be set to True, resulting in the eviction of pods running on that node. For details about node eviction, see Node-pressure Eviction.
- If the memory of a node is not enough, the following message will show:
- The value of MemoryPressure becomes True.
- When some pods on the node are evicted:
- You can see "The node was low on resource: memory" in the events of the evicted pods.
- You can see "attempting to reclaim memory" in the node events.
- The system OOM may behave abnormally. If such an error occurs, you can see "System OOM" in the node events.
Solution
- Check the node memory usage through the node monitoring data, identify the time when the exception occurs, and verify if there is any memory leak in the processes on the node. For details, see Checking the Node Monitoring Data.
Disk Pressure
Possible cause
Parameter |
Description |
Default Value |
nodefs.available |
Percentage of the available capacity in the file system used by kubelet. |
10% |
nodefs.inodesFree |
Percentage of available inodes in the file system used by kubelet. |
5% |
imagefs.available |
Percentage of the available capacity in the file system used by container runtimes to store resources such as images. |
10% |
imagefs.inodesFree |
Percentage of available inodes in the file system used by container runtimes to store resources such as images. |
5% |
Symptom
- If the available disk space on the node is less than the value of imagefs.available, the value of DiskPressure of the node becomes True.
- If the available disk space is less than the value of nodefs.available, all pods on the node will be evicted. For details about node eviction, see Node-pressure Eviction.
- If the disk space on the node is insufficient, the following message will show:
- The value of DiskPressure becomes True.
- If the disk space remains insufficient to meet the healthy threshold (defaulted at 80%) even after the image reclaim policy is triggered, you can see "failed to garbage collect required amount of images" in the node events.
- You can see "The node was low on resource: [DiskPressure]" in the events of the evicted pods.
- You can see "attempting to reclaim ephemeral-storage" or "attempting to reclaim nodefs" in the node events.
Solution
- View the node disk usage through the node monitoring data, identify the time when the exception occurs, and check if processes on the node are consuming excessive disk space. For details, see Checking the Node Monitoring Data.
- If a large number of files are not deleted from the node disks, delete these files.
- Restrict the ephemeral-storage configurations of the pods based on service requirements.
- Use cloud storage services instead of hostPath volumes.
- Expand the capacity of the node disks.
Abnormal kubelet
Possible cause
The kubelet process is not functioning properly or the kubelet configuration is improper. Typically, CCE has set up health checks for kubelet as a default configuration. There is a greater chance of startup failure if the configuration is incorrect.
Symptom
kubelet is inactive.
Solution
- Log in to the abnormal node and restart kubelet: (Restarting kubelet does not affect the running containers.)
systemctl restart kubelet
- Check whether the kubelet status becomes normal:
- If the kubelet status is still abnormal after the restart, log in to the node and view the kubelet logs:
- If there are error messages in the logs, find the cause by looking for specific keywords associated with the error.
- If there is an issue with the kubelet configuration, find the node pool that the node belongs to, click Manage in the Operation column, and make changes to the kubelet configuration.
Abnormal Runtime
Possible cause
The Docker or containerd configuration or process is not functioning properly.
Symptom
- Docker
- Docker is inactive.
- Docker is active and running, but the node is experiencing issues and not functioning properly, resulting in abnormal behavior. In this case, the docker ps or docker exec command fails to be executed.
- The value of RuntimeOffline of the node becomes True.
- containerd
- containerd is inactive.
Solution
- Log in to the abnormal node.
- Restart the runtime:
# Docker systemctl restart docker # Containerd systemctl restart containerd
- After the command is executed, check whether the running status is normal.
# Docker systemctl status docker # Containerd systemctl status containerd
- If the component status is still abnormal after the restart, check the component logs:
# Docker journalctl -u docker # containerd journalctl -u containerd
Abnormal NTP
Possible cause
The NTP process is abnormal.
Symptom
- chronyd is inactive.
- The value of NTPProblem becomes True.
Solution
- Log in to the abnormal node and restart chronyd:
systemctl restart chronyd
- After the restart, check whether the chronyd status becomes normal:
systemctl status chronyd
- If the chronyd status is still abnormal after the restart, log in to the node and view the chronyd logs:
journalctl -u chronyd
Abnormal Node Restart
Possible cause
The node is experiencing abnormal load.
Symptom
During the restart, the node is in the NotReady state.
Solution
- Check the time when the node was restarted:
last reboot
- View the node monitoring data and locate the abnormal resource based on the restart time of the node. For details, see Checking the Node Monitoring Data.
- Check the kernel logs and locate the fault based on the restart time.
Abnormal Node Network
Possible cause
The node is experiencing abnormal running status, incorrect security group configuration, or excessive network load.
Symptom
- The node cannot be logged in to.
- The node is in the Unknown state.
Solution
- If you cannot log in to the node, take the following steps to locate the fault:
- Check whether the node is running on the ECS console.
- Check whether the fault is caused by the execution failure of Cloud-Init of the ECS. For details, see Verifying Whether the ECS Can Be Logged In.
- Check the security group configuration of the node. For details, see Checking the Node Security Group.
- If the network load of the node is too high, perform the following operations:
- View the node networking through the node monitoring data and check whether the pods on the node are consuming excessive network bandwidth.
- Use network policies to control network traffic of the pods on the node.
Abnormal PLEG
Possible cause
The pod lifecycle event generator (PLEG) records different events in the lifecycle of a pod, such as the pod startup and termination. The error "PLEG is not healthy" is usually due to abnormal runtime processes on the node or issues with the systemd version on the node.
Symptom
- The node is in the NotReady state.
- You can see the following information in the kubelet logs:
skipping pod synchronization - PLEG is not healthy: pleg was last seen active 3m17.028393648s ago; threshold is 3m0s.
Solution
- Restart Docker or containerd and kubelet in sequence and then check whether the node is restored.
- If the node is not restored after the restart of the key components, restart the node. (Be cautious when restarting the node because it may cause interruptions to your services.)
Node Overloaded
Possible cause
The node resources are not enough for pod scheduling.
Symptom
- Insufficient CPUs in a cluster: 0/2 nodes are available: 2 Insufficient cpu
- Insufficient memory in a cluster: 0/2 nodes are available: 2 Insufficient memory
- Insufficient temporary storage space in a cluster: 0/2 nodes are available: 2 Insufficient ephemeral-storage
The scheduler determines that node resources are insufficient using the following calculation methods:
- Whether the CPUs of a node are insufficient: Total CPUs requested by a pod > (Total allocatable CPUs on the node - Total CPUs that have been allocated to the pods on the node)
- Whether the memory of a node is insufficient: Total memory requested by a > (Total allocatable memory on the node - Total memory that has been allocated to the pods on the node)
- Whether the temporary storage space of a node is insufficient: Temporary storage space requested by a pod > (Total allocatable temporary storage space on the node - Total temporary storage space that has been allocated to the pods on the node)
If the total resources requested by the pod exceed the allocatable resources on the node (after subtracting the allocated resources to the pods on the node), the pod will not be scheduled on that node.
Check the resource allocation details on the node:
kubectl describe node $nodeName
Pay attention to the resource allocation in the command output:
Allocatable: cpu: 1930m ephemeral-storage: 94576560382 hugepages-1Gi: 0 hugepages-2Mi: 0 localssd: 0 localvolume: 0 memory: 2511096Ki pods: 20 Allocated resources: (Total limits may be over 100 percent, i.e., overcommitted.) Resource Requests Limits -------- -------- ------ cpu 1255m (65%) 4600m (238%) memory 1945Mi (79%) 3876Mi (158%) ephemeral-storage 0 (0%) 0 (0%) hugepages-1Gi 0 (0%) 0 (0%) hugepages-2Mi 0 (0%) 0 (0%) localssd 0 0 localvolume 0 0
Specifically:
- Allocatable: specifies the total number of allocatable resources like CPUs, memory, and temporary storage on a node.
- Allocated resources: specifies the total number of resources like CPUs, memory, and temporary storage that have been allocated to the pods on a node.
Solution
- Delete unnecessary pods.
- Restrict the resource configurations of pods based on service requirements.
- Add more nodes to the cluster.
Restricted Node Scheduling with the node.kubernetes.io/route-unreachable Taint
Possible cause
The network infrastructure's route tables allow the container networks in a cluster that uses the VPC network model to be accessible. A newly created CCE node has network isolation support. If the node network is not functioning properly, the system will automatically add the node.kubernetes.io/route-unreachable taint to the node and remove it once the network is ready. If the node.kubernetes.io/route-unreachable taint remains for an extended period, it indicates abnormal network connectivity for the node.
Symptom
A newly created node is restricted for scheduling for a long time.
Solution
- If there are other normal nodes in the cluster, run the ping command to check the network connectivity between containers on different nodes.
Create a container for testing. In the following example, {node_ip} indicates the IP address of the abnormal node.
kind: Pod apiVersion: v1 metadata: name: nginx namespace: default spec: containers: - name: container-1 image: nginx:latest imagePullPolicy: IfNotPresent imagePullSecrets: - name: default-secret affinity: nodeAffinity: requiredDuringSchedulingIgnoredDuringExecution: nodeSelectorTerms: - matchExpressions: - key: kubernetes.io/hostname operator: In values: - {node_ip} schedulerName: default-scheduler tolerations: - key: node.kubernetes.io/route-unreachabe operator: Exists effect: NoSchedule
After the container is started, log in to another normal node and ping the IP address of the container. If the communication is abnormal, go to the next step.
- On the Route Tables page of the VPC console, check whether the node route has been added, whether the next hop type is cloud container, and whether the next hop is the node name. If the node route is present in the route table but the node is still unable to connect to the network, it suggests a potential problem with the underlying network. In such situations, submit a service ticket to the networking team for assistance.
- If the fault persists, submit a service ticket to CCE for troubleshooting.
Node Unavailable Due to OOM
Possible cause
Many containers are scheduled onto a node, using up all its resources and causing an OOM issue. This issue is primarily seen on nodes running the Docker container engine.
Symptom
If a node in the cluster is assigned too many containers, the node OS might crash, rendering the node unavailable. You may see the information similar to the following after logging in to the node with VNC.
Check the node events:
kubectl describe node {nodeName}
Pay attention to the abnormal node events in the output.
Solution
If the resources on a node are not enough for pod scheduling, reduce the node load through either of the following ways:
- Reset the faulty node.
